[RE-wrenches] Wattsun Tracker Foundations

Ken Schaal Ken at commonwealthsolar.com
Sat Oct 27 10:50:03 EDT 2012


Our first tracker job was for Y2K here in central Va. --a lot of red clay soils, especially down 3'+. The client had been in the 8' Satellite dish  business. He suggested using his backhoe to dig a ' chicken foot'   foundation--3 horizontal footings, as deep and as long  as you want. This leaves a central space ,where the footings merge,  for the 8-10 " , schedule 40 or 80 pipe. We typically make the feet 4' -5'deep--especially at the bottom of the pole-- and 6' long and 12 " wide, with plenty of rebar circling the pipe and extending into the feet, at 1'  increments of depth. Rebar is cheap so use plenty of it, and use a 3-4000 psi concrete , as dry as possible.
The windiest location has probably taken 70-100 mph gusts--enough to take the roof off the nearby farm building, and necesitate the elevation actuator to need upgrading-- but the foundation is unmoved.

One little trick is to get your own 6" box beam --less expensive than shipped from Wattsun-- and make it a little longer than typical in order to allow a 2" space between modules to relieve the air pressure. We also like to have the manual control so the array can be set flat, although that was not activated by the owner during the last several wind events. Hence the need to upgrade the elevation actuator---------

Never had it engineered tho, so use your own judgement.

Ken
CommonWealth Solar
Ashland , Va
  ----- Original Message -----
  From: Solarguy 
  To: 'RE-wrenches' 
  Sent: Saturday, October 27, 2012 10:19 AM
  Subject: Re: [RE-wrenches] Wattsun Tracker Foundations


  We've installed a number of AZ225s and big Zomeworks trackers to date. There are a number of companies that do foundation pier drilling but only a handful that have the capacity for a 36" pier. Even fewer will drill thru rock if it's down there. 

  Water must be pumped out when it starts to collect and dealing with that pita is something to take up in advance with the cement contractor. 

   

  Jim Duncan

  North Texas Renewable Energy Inc

  www.ntrei.com 

  NABCEP PV 031310-57

  TECL-27398

  ntrei at 1scom.net 

  817.917.0527

   

   

   

  From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Ryan Harkins
  Sent: Friday, October 26, 2012 2:36 PM
  To: RE-wrenches
  Subject: [RE-wrenches] Wattsun Tracker Foundations

   

  Hey Wrenches,

   

  I planning some AZ-225 tracker installs, and I would like to avoid full excavation for slab/pier type and opt for the drilled pier option.  The pier is supposed to be 30-36" diameter and 9.5' deep.  This would require a terex reedrill or similar rig.  If you know of a firm with that equipment in Wisconsin please contact me off list.

   

  Also, one site has a high water table, so any tips on pouring in that environment would be welcomed.

   

  Thanks

   

   

  Ryan Harkins
  NABCEP Certified Solar PV Installer /
  Project Manager
           






------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: RE-wrenches at lists.re-wrenches.org

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20121027/082c4ceb/attachment-0001.htm>


More information about the RE-Wrenches mailing list