There is a potentiometer on the board of the IOTA chargers that used to be
assessable through a hole in the cover. I adjusted a new one two weeks ago
and had to open it up to get at the pot. Adjusts up 15.6VDC with plug in and
14.8 with the jumper plug out. Some of the older models would adjust up to
16.5V and the new ones may as well, I did not need that value with the last
charger.
These are very simple units that could be considered a fire hazard in the
wrong place/hands. I use for the lowest of the low budgets that are way, way
off-grid and always explain the caveat to not have flammable things anywhere
close to it. I had a couple of Todds spark off a number of years ago. Caused
some excitement.
-Dave
David Palumbo
Independent Power LLC
462 Solar Way Drive
Hyde Park, VT 05655
www.independentpowerllc.com
NABCEP Certified PV Installer
Vermont Solar Partner
24 Years Experience, (802) 888-7194
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William
Dorsett
Sent: Monday, October 15, 2012 2:27 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Off-grid non-inverter battery charger
recommendations?
Thanks Aaron, but I need one that goes to 15.5 or 16V for equalizing the
bank. Just got this back from Iota:
"Iota does not make any chargers that go to 15 volts output for equalizing.
Thank you
Iota Engineering"
Xantrex TruCharge 20 at least has an equalize setting, though I don't know
how adjustable it is.
Bill Dorsett
Sunwrights
Manhattan, KS
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Aaron
Mandelkorn
Sent: Monday, October 15, 2012 10:24 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Off-grid non-inverter battery charger
recommendations?
Check out Iota.
Aaron Mandelkorn
NABCEP Certified PV Installer
Renewable Energy Outfitters
Box 65 Salida, CO. 81201
(970)596-3744
reosolar at gmail.com
www.reosolar.com
On Oct 15, 2012, at 9:14 AM, William Dorsett wrote:
What brand recommendations do the group have for an battery charger to be
plugged into a genset? Used to be Todd but at some point they lost favor.
Thanks all.
Bill Dorsett
Sunwrights
1715 Leavenworth
Manhattan, KS
785/539-1956 Home/Office
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20121015/15e87d6a/attachment-0001.htm>
More information about the RE-Wrenches
mailing list