[RE-wrenches] Solar Log Scematics
Glenn Burt
glenn.burt at glbcc.com
Sat Oct 6 08:58:02 EDT 2012
This is only if you are using the inverter RS-485 piggy back board that is
3rd party provided, not the one you get from SMA.
If you are using the SMA manufactured RS-485 piggy back interface board,
only 3 conductors are used! The 4th conductor used in the above case
supplies +12 VDC, and is not an SMA standard.
Solar Log manual, Section 4.2.3, pp23:
Solar Log SMA
1 2
3 5
4 7
-Glenn
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of David Katz
Sent: Saturday, October 06, 2012 2:09 AM
To: Max Balchowsky; RE-wrenches
Subject: Re: [RE-wrenches] Solar Log Scematics
Hi Max,
For an RS-485 connection, Solar-log terminal 1 goes to SMA terminal 2,
Solar-Log terminal 3 goes to SMA terminal 5, Solar-Log termional 4 goes to
SMA terminal 7.
The manual is very clear. You can look at it online or download it at:
http://www.solar-log.net/index.php?eID=tx_mm_bccmsbase_zip
<http://www.solar-log.net/index.php?eID=tx_mm_bccmsbase_zip&id=1690614414506
fc88559195> &id=1690614414506fc88559195
I am having great luck with 3 SMA inverters connected to a Solar-Log 1000.
David
David Katz
CTO & Founder
AEE Solar Inc
P: 707 825-1200
F: 707 825-1202
dkatz at aeesolar.com
www.aeesolar.com
DISCLAIMER:
This communication, along with any documents, files or attachments, is
intended for the use of only the addressee and contains privileged and
confidential information. If you are not the intended recipient, you are
hereby notified that any dissemination, distribution or copying of any
information contained in or attached to this communication is strictly
prohibited. If you have received this message in error, please notify the
sender immediately by e-mail reply and destroy the original communication
and its attachments without reading, printing or saving in any manner.
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Max
Balchowsky
Sent: Friday, October 05, 2012 9:35 AM
To: RE-wrenches
Subject: [RE-wrenches] Solar Log Scematics
Does anyone have schematics for wiring the Solar Log monitor to talk to the
SMA 5k
I've hooked one up in Hawaii, with the wireless card in the 5k, but it's not
talking to the inverter.
Also, I have another to hard wire but I can't find information anywhere to
know what pins on the solar
log to tie to the 2, 5, 7 pins in the Sunny Boy. Their tech support seems to
be non existent.
Max Balchowsky
Design Engineer
SEE Systems
1048 Irvine Ave Suite 217
Newport Beach, Ca. 92660
760-403-6810