When in doubt .. ask the manufacturer.
Dan
--- On Mon, 8/27/12, Kirpal Khalsa <solarworks at gmail.com> wrote:
From: Kirpal Khalsa <solarworks at gmail.com>
Subject: Re: [RE-wrenches] Ilsco SGB bonding lug
To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Date: Monday, August 27, 2012, 6:42 PM
Benn...it looks like that lug has "stainless hardware for corrosion resistance" as stated on the brochure....That would be the biggest consideration as David Brearly mentioned earlier in regards to rust potential. Stainless hardware and tin plating is equivalent to the WEEB lugs....Tin plating and stainless hardware is as good as anything else available as far as outdoor ratings are concerned.....
I see your point that it is not explicitly stated for outdoor use....however being marketed for use with solar panels also seems to imply rather obviously that it is outdoor rated.....in my unofficial opinion.
--
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer
On Mon, Aug 27, 2012 at 4:11 PM, benn kilburn <benn at daystarsolar.ca> wrote:
Thanks for the feedback Wrenches, lots of interesting comments,
However I'm still wondering…..How does one confirm that it is specifically approved for outdoor use? Other than assuming it is implied (because it is 'marketed' as a solar lug). As far as I can tell UL 467 does not imply "outdoor rated" as the aluminum lug "GBL-4" is also UL467 listed. See here…GBL LAY-IN AL/CU.
As well, and as Gary pointed out with his second link, for a module bonding/grounding method to be acceptable, it must be recognized by the module manufacturer, no?Which means that any new bonding product on the market must have the blessing of each mod mfgr.
(by way of letter or mention in its install manual). I have come across inspectors that actually look for this.
Jason, you wrote "I like the looks of that lug. However, I've been using WEEBs too long to go back now." I agree, and i'm not looking to replace weebs with these, but these certainly seem to have a place in the What do you use for the bonding connection from the ?rails?
This SGB lug was suggested for this purpose as well.
BennDayStar Renewable Energy Inc. www.daystarsolar.ca * Ph: 780-906-7807
Construction Electrician Solar Photovoltaic Systems CertifiedCertificate # 0007SHAVE A SUNNY DAY
On 27/08/12 2:35 PM, "Gary Willett" <gary at icarussolarservices.com> wrote:
Here's the Ilsco
listing from UL, where it's classed as "Grounding and Bonding
Equipment":
http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?name=KDER.E34440&ccnshorttitle=Grounding+and+Bonding+Equipment&objid=1074099002&cfgid=1073741824&version=versionless&parent_id=1073988940&sequence=1
The GuideInfo for Grounding & Bonding Equipment lists:
Grounding and Bonding for
Photovoltaic (PV) Systems — Grounding and bonding
equipment intended for use in PV systems are additionally
investigated in combination with the PV module/panel (see
QIGU) to the applicable requirements for such products.
Installation instructions provided with the PV system (see
QIGU) identify the specific grounding and bonding device that
has been investigated and intended for use with that system.
http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?&name=KDER.GuideInfo&ccnshorttitle=Grounding+and+Bonding+Equipment&objid=1074098839&cfgid=1073741824&version=versionless&parent_id=1073988940&sequence=1
Regards,
Gary Willett, PE
On 8/27/2012 3:20 PM, David Brearley wrote:
Yes, sorry. I wasn't speaking of this lug...I like the
redesign. Looks quicker and easier and robust.
On Aug 27, 2012, at 3:17 PM, Jason Szumlanski wrote:
Yeah, but this one is marketed as a
solar bonding lug. I think it's safe to say that it
appropriately rated for outdoor use. It's always good to
double-check, of course.
Jason Szumlanski
Fafco Solar
On Mon, Aug 27, 2012 at 4:11 PM,
David Brearley <david.brearley at solarprofessional.com>
wrote:
Some of the aluminum
lugs are indoor-rated. They have a set screw will
rust in an outdoor environment. That's one of the
classic John Wiles slides. I'd just watch out for
that....
On Aug 27, 2012, at 12:53 PM, Brian
Mehalic <brian at solarenergy.org> wrote:
I believe the UL467 listing means
that it is rated for direct
burial/outdoor use.
Brian Mehalic
NABCEP Certified Solar PV
Installer™ R031508-59
IREC ISPQ Certified Affiliated
Instructor/PV US-0132
PV Curriculum Developer and
Instructor
Solar Energy International
http://www.solarenergy.org
.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-----Inline Attachment Follows-----
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20120827/7c249dc1/attachment-0001.htm>
More information about the RE-Wrenches
mailing list