[RE-wrenches] High L16 voltage situation
John DeBoever
jdeboever at trojanbattery.com
Tue Jul 17 17:58:33 EDT 2012
Nathan,
Interesting controller situation...
I recommend you contact Morningstar tech support center , (215) 321-4457 for support. Ask for Adams.
Hope they will clear this out.
John
John F. DeBoever
Global Technical & Projects Director - Renewable Energy
Trojan Battery Company
12380 Clark Street
Santa Fe Springs, CA 90670
Tel: +1-562-236-3000 Ext. 3139
Cell: +1-845-514-7600 - NY office time zone: USA EST (GMT-5)
Skype: john.f.deboever
Fax: +1-562-236-3239
jdeboever at trojanbattery.com<mailto:jdeboever at trojanbattery.com>
www.trojanbattery.com<http://www.trojanbattery.com/>
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Nathan Jones
Sent: Tuesday, July 17, 2012 5:45 PM
To: re-wrenches at lists.re-wrenches.org
Subject: Re: [RE-wrenches] High L16 voltage situation
John
Two 12 volt nominal panels wired in parallel.
Battery configuration is series/parallel at 12 volts nominal Controller (all of them) have been 12 volt nominal PWM VPM is 17.7 VDC IPM is 7.91 Open circuit voltage was down about 1 volt due to heat.
I have not pulled the batteries down much below surface charge so max amperage I have observed going back into the batteries has been 5 amps but it tapers off within about 6 minutes as the controller regulates back to float. Absorb and float are at 15.6VDC in all cases with all the controller combinations unless I add the AGM jumper to the controller which does lower absorb and float voltage to Morningstars published settings with the one controller I attempted it with.
Nathan Jones
------------------------------
On Tue, Jul 17, 2012 3:41 PM CDT John DeBoever wrote:
>Nathan,
>
>
>
>Maybe the devil is in the details... Maybe the controller is confused and "sees" a 24V system... Just thinking...
>
>Kindly clarify few points:
>
>o At which voltage the PV array is configured? 2x PV modules in parallel 12V or 2x PV modules in series?
>
>o Does the SunSaver Morningstar controller at the site is a 12V or a 24V version?
>
>o What is the Vmp of the PV module?
>
>
>
>John
>John F. DeBoever
>Global Technical & Projects Director - Renewable Energy Trojan Battery
>Company
>
>12380 Clark Street
>Santa Fe Springs, CA 90670
>Tel: +1-562-236-3000 Ext. 3139
>Cell: +1-845-514-7600 - NY office time zone: USA EST (GMT-5)
>Skype: john.f.deboever
>Fax: +1-562-236-3239
>jdeboever at trojanbattery.com<mailto:jdeboever at trojanbattery.com<mailto:jdeboever at trojanbattery.com%3cmailto:jdeboever at trojanbattery.com>>
>www.trojanbattery.com<http://www.trojanbattery.com/<http://www.trojanbattery.com%3chttp:/www.trojanbattery.com/>>
>
>
>
>
>
>-----Original Message-----
>From: re-wrenches-bounces at lists.re-wrenches.org
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Nathan
>Jones
>Sent: Tuesday, July 17, 2012 4:36 PM
>To: re-wrenches at lists.re-wrenches.org
>Subject: Re: [RE-wrenches] High L16 voltage situation
>
>
>
>
>
>
>
>Mick,
>
>Pesky is a nicer term than I had been using. I clamped the charge circuit and watched the amperage come in on final phase of absorb then drop to zero. (Since the voltage stayed at the same 15.6VDC when the amperage dropped off there was some current but my meter could not read it. That is the pesky part. Everything seems to be behaving as it should be. I will try the splitting of the parallel battery strings and check each string. And as Jay suggested, take a different brand of controller with me next time. What is frustrating is this should be as simple as things can get and yet it is so perplexing. Keeps me humble.
>
>Thanks,
>
>Nathan Jones
>
>
>
>
>
>------------------------------
>
>On Tue, Jul 17, 2012 11:19 AM CDT Mick Abraham wrote:
>
>
>
>>Hi, Nathan~
>
>>
>
>>Your pesky overcharge situation sounds like a real pain given the long
>
>>commute. 15.6 volts on a "12 volt" battery implies zero restriction of
>
>>the incoming energy, so this looks like a controller problem...or
>>maybe
>
>>it's a wiring problem that prevents proper controller operation. Make
>
>>sure there's a -12 in the model number for your Morningstar Sunsaver
>
>>controls, as those are voltage specific.
>
>>
>
>>Eliminate as many variables as possible, Nathan: unhook two of the 6v
>
>>L-16's, leaving only two in a 12 volt string. Connect only one PV
>
>>module through the 12v controller and see if the voltage will regulate properly.
>
>>If you have a clamp style DC ammeter, clip around one lead in the
>
>>charge circuit & read the amps with good sun. If the battery voltage
>
>>continues high while you see ~ 7-8 amps PV charge...the controller is
>
>>failing to do its job.
>
>>
>
>>Jolliness,
>
>>
>
>>Mick Abraham, Proprietor
>
>>www.abrahamsolar.com<http://www.abrahamsolar.com<http://www.abrahamsolar.com%3chttp:/www.abrahamsolar.com>>
>
>>
>
>>Voice: 970-731-4675
>
>
>
>_______________________________________________
>
>List sponsored by Home Power magazine
>
>
>
>List Address:
>RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches<mailto:RE-wrenches at lists.re-wrenches.org%3cmailto:RE-wrenches at lists.re-wrenches>.
>org>
>
>
>
>Options & settings:
>
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>
>
>List rules & etiquette:
>
>www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette<http://www.re-wrenches.org/etiquette.htm%3chttp:/www.re-wrenches.org/etiquette>.
>htm>
>
>
>
>Check out participant bios:
>
>www.members.re-wrenches.org<http://www.members.re-wrenches.org<http://www.members.re-wrenches.org%3chttp:/www.members.re-wrenches.org>>
>
>
>
>
>
>
>This e-mail message and any attachments that accompany it may contain
>information that is confidential, privileged, or protected from disclosure.
>It is intended solely for the use of the individual(s) to whom it was
>intended to be addressed. If you have received this e-mail by mistake,
>or you are not the intended recipient, any reading, disclosure, copying
>or other use of this communication is strictly prohibited. If you have
>received this communication in error, please immediately advise the
>sender at their phone number listed above, or by electronic mail, and
>also permanently delete the original and all copies of this e-mail and any attachments from all locations. Thank you.
>
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
This e-mail message and any attachments that accompany it may contain
information that is confidential, privileged, or protected from disclosure.
It is intended solely for the use of the individual(s) to whom it was intended
to be addressed. If you have received this e-mail by mistake, or you are not
the intended recipient, any reading, disclosure, copying or other use of this
communication is strictly prohibited. If you have received this communication
in error, please immediately advise the sender at their phone number listed
above, or by electronic mail, and also permanently delete the original and all
copies of this e-mail and any attachments from all locations. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20120717/b004f1ce/attachment-0001.htm>
More information about the RE-Wrenches
mailing list