[RE-wrenches] Wood boiler ignition issue
Dana
dana at solarwork.com
Mon Mar 26 16:05:11 EDT 2012
Sorry Kris I got interrupted and sent this early.
Repair options - replace inverters with cleaner sine wave inverters, replace
controller in wood boiler, or add a small 120-120 VAC transformer that is
relay controlled so it is only on when the boiler is called for. That last
option is not really responsible but that and adding a PV module [or 2] to
the array to offset the load may be the least expensive option.
Thanks
Dana Orzel - Great Solar Works, Inc - E - dana at solarwork.com - V
970.626.5253
F - 970.626.4140 C - 970.209.4076 web - www.solarwork.com
"Responsible Technologies for Responsible People since 1988"
P Please consider the environment before printing this email
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dana
Sent: Monday, March 26, 2012 12:59 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Wood boiler ignition issue
Yes with Rogers-White controllers they do not like how the sine wave crosses
the X axis in the "sine" wave.
It is an Inverter sine wave quality problem. I have had this problem with
Trace SW series too. Even with the 56 step sine wave it was an issue.
-------------- next part --------------