[RE-wrenches] meter pan?
Dave Click
daveclick at fsec.ucf.edu
Tue Jan 24 09:49:01 EST 2012
I guess someone could argue that 690.15 would require a disconnect on
both sides of that meter, but for this install, the line-side disconnect
would immediately trip the inverters offline, so you can't really say
that the meter is "energized from more than one source" like a DC
disconnect would be. I'd say your fused disconnect would be all you
need. Does your utility/program really allow you to put the production
meter in the basement?
Is anyone using the Milbank load-tap connectors yet? Part# K4977-INT
allows for up to a 100A load-side connection in a Milbank 200A meter
socket. It looks like it would be the best/easiest way to make these
connections with caveats: get utility's permission before you open the
socket and pull out the meter, and be wary of the very live voltage on
the line side terminals.
http://solarprofessional.com/article/?file=SP5_1_pg20_TheWire_3
(hat tip to Eric Thomas, who I now see posted about this last April-- I
don't see that anyone's commented on it since)
Also, note that the tap rules don't apply here, so you're better off
calling it something other than "tap" when talking with your inspector.
-Dave
On 2012/1/24 9:14, Allen Frishman wrote:
> Wrencher's,
> I am having a good debate with a fellow solar installer regarding an NEC
> requirement to isolate a meter between two disconnecting means adjacent
> to the meter when grid connecting via a tap. My thought is that if we
> have a load center with breakers to combine multiple inverters on the
> roof, the PV meter can be located in the basement between the roof load
> center and a fused disconnect adjacent to the tap with no need for a
> disconnect next to the meter on the load center side of the meter. Can
> anyone reference a section in the code that requires a disconnecting
> means adjacent to both sides of the meter? The meter I am referencing
> simply records the total kWh's of the solar system as required by the
> State incentive program.
>
> All feedback is appreciated.
>
> /Al Frishman/
> AeonSolar
>
> /(917) 699-6641 <tel:%28917%29%20699-6641> - cell/
> /(888) 460-2867 <tel:%28888%29%20460-2867>/
> /www.aeonsolar.com <http://www.aeonsolar.com/>/
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options& settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules& etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
More information about the RE-Wrenches
mailing list