[RE-wrenches] Grounding Separately Derived AC System
Jesse Dahl
dahlsolar at gmail.com
Tue Jan 24 00:54:38 EST 2012
I agree and read it the same way. Not a separately derived system.
Jesse
Sent from my iPhone
On Jan 23, 2012, at 7:13 PM, "Dave Palumbo" <dave at independentpowerllc.com> wrote:
> Regarding NEC Article 250.30 does Informational Note #1 mean that a standard (no battery) grid-tied PV system is not a Separately Derived System?
>
> I’m primarily interested on the consensus view of Bonding the Neutral (grounded conductor) to Equipment Ground in a 60 Amp Fused Disconnect located between the 240VAC inverter output and AC point of connection on the load side of the meter in the service disconnect enclosure in a supply side connected PV system.
>
> 250.30 Informational Note 1 reads: “An alternate ac power source, such as an on-site generator, is not a separately derived system if the grounded conductor is solidly interconnected to a service-supplied system grounded conductor…” I believe a PV system meets that description as the Neutral stays connected at all times.
>
> My interpretation is that a standard net-metered PV system is therefore not a separately derived system and the Neutral should not have a bonding jumper to equipment ground in the Fused Disconnect.
>
> Is this the correct interpretation?
>
> David Palumbo
> Independent Power LLC
> 462 Solar Way Drive
> Hyde Park, VT 05655
> www.independentpowerllc.com
> NABCEP Certified PV Installer
> Vermont Solar Partner
> 24 Years Experience, (802) 888-7194
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20120123/71297f57/attachment-0001.htm>
More information about the RE-Wrenches
mailing list