[RE-wrenches] Request for Gennie Recommendation
Jason Szumlanski
Jason at fafcosolar.com
Mon Jan 16 09:57:25 EST 2012
If the water cooled models are similar to the <=20kW air cooled models,
the ATS is not integrated, but there is a controller that does not allow
a two wire generator start circuit out of the box. However, there is a
Generac rep named Bob Cramer that supplied my with a wire kit and
instructions to bypass the controller and make a two-wire start relay
work. If you need to contact him, send me a private email and I'll
provide his contact information.
I would not recommend the air cooled models, especially in warmer
climates. They are remarkably affordable, however, and should work fine
in occasional standby service.
Jason Szumlanski
Fafco Solar
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Howie
Michaelson
Sent: Monday, January 16, 2012 9:49 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Request for Gennie Recommendation
Allan,
I have heard from a generator sales / service friend that the water
cooled
Generac gennies (I believe 20 kW and up) are totally different animals
than the standard Generac gennies. From personal experience and
word-of-mouth I wouldn't touch the standard generac machines, but the
water cooled ones seem to be good machines, although I have no personal
experience with them. Not sure if they come with the integrated ATS
which
have caused major headaches for me in off-grid setup.
Howie
--
Howie Michaelson
NABCEP Certified Solar PV Installer(tm)
Catamount Solar, LLC
Renewable Energy Systems Sales and Service
VT Solar Electric & Hot Water Incentive Partner
http://www.CatamountSolar.com
802-272-0004
On Mon, January 16, 2012 7:25 am, Comet Systems wrote:
> Allan,
> First, I'm a Generac sales & service dealer so I have an obvious bias.
> The Olympian brand are made by Generac for caterpillar.
>
> Anything under 20KW will be residential and will be designed for short
> runs. The Generac 6KW Ecogen is very well suited for your needs, as it
is
> built for long run applications and features an oversize oil pan to
help
> with oil breakdown and cooling issues.. If you need bigger than that,
I
> would look to a QuietSource 20KW. Low speed, long run commercial
quality
> but very cost effective and well supported.
>
http://www.generac.com/Commercial/QuietSource/Products/QuietSource_Serie
s_22_kW/
>
> Let me know if you need additional information
>
>
>
>> Re Olympian (made by Caterpillar): the smallest model sold in this
>> country
>> is a 25kW, well larger than we need.
>>
>> Re Generac: while I am quite impressed with the 6kW EcoGen unit,
that's
>> a
>> special model, developed for the purpose, and too small for this
>> application. I'm hesitant to use one of their standard units.
>>
>>
> --
> Chris Mason
> President, Comet Systems Ltd
> masonc at cometsystems.co
> www.cometsystems.co
> Cell: 264.235.5670
> Int: +1305.767.2094
> Skype: netconcepts
> _______________________________________________
More information about the RE-Wrenches
mailing list