Jeremy:

Bingo!  You have discovered the hard truth of grid tie with battery point 
of connection compliance (GTWB POC).  Your inverter will through-transfer 
up to 60 Amps (A), so to use all of that capability, you should feed it 
with 60A.  However, you are not allowed to feed the inverter with greater 
than 40A dedicated over-current protection (OCPD).  The arithmetic is:

Buss rating:  200A
Allowed total buss feed:  200A X 120% = 240A
Main breaker: 200A
Allowed PV feed:  240A-200A= 40A*


If you can downgrade the main breaker to 150A you can back feed up to 
90A.  The arithmetic then is:

Buss rating:  200A
Allowed total buss feed:  200A X 120% = 240A
Main breaker: 150A
Allowed PV feed:  240A-150A= 90A

Downgrading the main breaker is not easy.  Most meter/main/combos (MMCs) 
will not allow the downgrade-- there is not a 150A breaker made that is 
designed and listed to fit in the 200 A panel.  I have contacted various 
manufacturers and requested that 200 (MMCs) be made that will readily 
accept a 150A main breaker, but large corporations do not seem to care 
about the needs of a small part of the market..

I had found a 200 A MMC that I could downgrade the main breaker to 150 A, 
but not easily.  The fit was not perfect -- I had to modify the hold down 
bracket, but it passed inspection.  Technically I suppose the MMC was no 
longer compliant with the listing once I modified it, but sometimes you 
gotta do what you gotta do.

Good Luck.

William Miller

* PS:  I believe the 2011 NEC has an exception that applies, but I do not 
believe any jurisdictions are using that code.  I have convinced my local 
building officials to pre-adopt certain future code sections.  Maybe you 
can make the case to your local inspectors.  Meet with them, explain the 
limitations of the XW as far as intertie amperage and maybe they will allow 
use of a 60A breaker.