[RE-wrenches] Point of Connection 705.12D2 Exception

Kent Osterberg kent at coveoregon.com
Sun Dec 30 19:56:35 EST 2012


If you are using the 2011 NEC, 705.12(D)(2) has an exception to the 120% 
rule for inverters with energy storage to allow for operation of loads.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882

On 12/30/2012 4:27 PM, Jeremy Rodriguez- All Solar Inc. wrote:
> I'm concerned that the inspector will not allow a 60A back fed breaker in the 200A main panel as it exceeds the 120% rule
> Jeremy
> Sent via BlackBerry. Sorry for typos and shorthand!
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>



More information about the RE-Wrenches mailing list