Erika, I think the takeaway here is that the Island only has that surge
power capacity on the protected load side- you wouldn't see this surge
on the utility side. SMA should be able to provide this sort of
documentation for you.
On 2012/10/18 9:38, Erika Weliczko wrote:
> Greetings all.
>
> I recently received this back regarding an interconnection application
> proposing a Sunny Island 6048 and a SB7000:
>
> “we have to rate the system at the max output of the inverters, and
> since that battery backup has an inverter that can export 11kW, (albeit
> for 3 seconds) I have to review the system for a total of 18kW.�
>
> This is a new one on me. I might argue that the SB7000 is upstream of
> the SI6048 and really the SI6048 is the point of interconnection, so the
> SB7000 is irrelevant. And 3 seconds is not really continuous operation.
>
> It seems that batteryless inverters show continuous output ratings,
> though I know there are some that specify a larger than expected OCP for
> various reasons, but that is not what the utility cares about.
>
> Any insights here?
>
> Thanks,
>
> Erika
>
> REpower SOLUTIONS
>
> www.repowersolutions.com
>
> P: 216.268.2275
>
> C: 216.402.4458
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
More information about the RE-Wrenches
mailing list