[RE-wrenches] weak voltage
mac Lewis
maclewis1 at gmail.com
Mon Oct 15 08:54:12 EDT 2012
Hmmm,
This had factory installed bussing. I will pull it off and clean it up.
Thanks. I suppose that something like this be invisible to an Amp hr
meter.
On Sun, Oct 14, 2012 at 11:01 PM, William Miller <william at millersolar.com>wrote:
> Mac:
>
> We had a similar problem with a large bank of IBE 2 volt cells. The
> batteries had to be removed the same day they were installed and then
> reinstalled the next day. They sat outside for one night. The flags
> acquired an invisible but insidious corrosion that caused problems getting
> and keeping a charge. Now we insist on cleaning each flag and eyelet no
> more than 10 minutes prior to contact.
>
> William Miller
>
>
>
> At 09:41 PM 10/14/2012, you wrote:
>
>> Hi wrenches,
>>
>> About 2 months ago, we installed an off-grid Sunny Island System. Here
>> are the specs:
>>
>> 8.82 kW PV
>> SunnyBoy 8000
>> 2 x Sunny Island 5048 Inverters
>> 2490 Ahr SolarOne HUP batteries at 48V
>> 30 kW Cummins Propane Generator
>>
>> We are having an issue that I am having a hard time figuring out. We are
>> getting sagging battery voltage, and can't seem to keep the battery voltage
>> and specific gravity where we want it. In addition, I have equalized these
>> batteries 4 times this past month, and the specific gravity gets to about
>> 1.25-1.26 maximum. I have slowly eased up the boost, absorb and equalize
>> voltage setpoints, to try to get the battery a better charge, but it
>> doesn't seem to help. The Sunny Islands don't seem to have any issue
>> getting these batteries up to the equalization voltage, or any of the other
>> voltage set points. I have checked for loose connections, all look good
>> here.
>>
>> The SOC monitor on the Sunny Island master, calculates that we are
>> staying between 70-95% SOC on a daily basis, and yet the battery voltage
>> has dropped below readable level a few times(I believe this is below 41V).
>> I equalized at 62 V for 4 hours and had the same result of nonimpressive
>> sepecific gravity and saggy voltage under small load. After we leave from
>> equalizing the batteries, things seem to be OK for a while and then we
>> start having issues again. We are tripping a 250A battery breaker, and
>> getting low voltage errors on the SI, yet SOC looks good.
>>
>> Right now I have the set points programmed per SolarOnes advice as:
>>
>> Boost Voltage= 2.46 V/cell
>> Full Charge Voltage = 2.46V/cell
>> Equalize Voltage = 2.54V/cell
>>
>> Thanks in advance for any ideas that you may have.
>>
>>
>>
>> --
>>
>
> ______________________________**_________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.**org<RE-wrenches at lists.re-wrenches.org>
>
> Options & settings:
> http://lists.re-wrenches.org/**options.cgi/re-wrenches-re-**wrenches.org<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>
> List-Archive: http://lists.re-wrenches.org/**pipermail/re-wrenches-re-**
> wrenches.org<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.**htm<http://www.re-wrenches.org/etiquette.htm>
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
--
Mac Lewis
*
"Yo solo sé que no sé nada." -Sócrates
*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20121015/8c9a53d3/attachment.htm>
More information about the RE-Wrenches
mailing list