Thanks Allan,

I always value your insight. There is a TriMetric on this system but I'm looking at the FM80. I wrestled with the idea that the systems are connected as the circuits between the two banks are not complete. However, as soon as I made the connections the voltage on the new bank dropped and the old bank "seemed" to be rejuvenated. Yes, it could simply be an issue of  I didn't witness a "drop" but before and after voltage was off by about 2 volts (down from 25 to 23) according to the charge controller. Not a lot but enough to raise an eyebrow.

Eric
  ----- Original Message ----- 
  From: Allan Sindelar 
  To: RE-wrenches 
  Sent: Thursday, October 11, 2012 4:00 PM
  Subject: Re: [RE-wrenches] Marine battery bank switch


  Eric,
  It still doesn't make sense to me. Unless you have a complete circuit, the banks are not in parallel, and your switch on the positives prevents a complete circuit of both at the same time. Common negatives should not be an issue - after all, in a standard off grid system, the DC - and the AC neutral are common to the same ground rod and thus equipment bonding. A Trimetric TM2025 has a second battery voltage sense function that requires the negatives be common; mine tells me the voltage of my main 24V system and my 12V generator starting battery, and all works well.

  So I question your perception that one is stronger and the other weaker. How do you perceive this new difference, and could it simply be a error in perception? One issue with a switch on two banks is that you can't use a single amp-hour meter, such as a TriMetric. So I would tend to place less value on subjective perception without the metrics to back it up. 
  Allan


  Allan Sindelar
  Allan at positiveenergysolar.com
  NABCEP Certified Photovoltaic Installer
  NABCEP Certified Technical Sales Professional
  New Mexico EE98J Journeyman Electrician
  Founder and Chief Technology Officer
  Positive Energy, Inc.
  3209 Richards Lane (note new address)
  Santa Fe, New Mexico 87507
  505 424-1112
  www.positiveenergysolar.com 





  On 10/11/2012 4:23 PM, SunHarvest wrote:

    I recently installed a Blue Sea 4-way marine battery switch to switch between two battery banks, one new bank and one old bank. I was hesitant to connect the negative home-runs from both banks onto one common bus (connected directly to a ground rod), which then connects back to the DC load center at the inverter. But that's how I was advised to wire it by an electrician friend. 

    It appears now that the newer bank was performing quite a bit better prior to being connected to the marine switch (and neg lead to the neg bus) and the old bank is now performing better than before. I think my electrician buddy was incorrect and that even the positive leads being on a switch and neg lead on a neg bus, the banks are still, to some extent, effectively paralleled and that the new bank is being pulled down by being indirectly connected to the old bank.

    Thoughts and advice on how to correct the wiring if needed?

    Sorry to ask such a simple question, I'm just a little rusty on off-grid.

    Thanks guys.

    Eric Stikes
    SunHarvest Solar


     

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: RE-wrenches at lists.re-wrenches.org

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20121011/eb101a2b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Signature.jpg
Type: image/jpeg
Size: 11628 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20121011/eb101a2b/attachment.jpg>


More information about the RE-Wrenches mailing list