[RE-wrenches] SunnyIsland - was AC coupling and Outback inverters
Dave Click
daveclick at fsec.ucf.edu
Fri Oct 5 09:00:31 EDT 2012
Check out the new SMA Smartformer, though I'm not sure whether it's
actually shipping yet. I'm thinking about this for my house eventually
(SB5000US).
http://www.sma-america.com/en_US/products/off-grid-and-back-up-solutions/smartformer-for-sunny-island.html
Alternatively, the new SMA TL inverters (at least the 3, 4, and 5kW
units according to the press release) have an "Emergency Power Supply"
function that can provide backup power (12A?) during the day when the
grid is down. This may meet your customer's requirements. No batteries
required, though since the TLs require ungrounded arrays, you may need
to rewire the existing array to be compliant with 690.35 (PV Wire or
raceway).
On 2012/10/5 8:41, Kirk Herander wrote:
> One Question: Output of the SunnyBoy is 240vac. So this is fed to the
> critical load panel, of which the SunnyIsland 120 vac output is fed to.
> So we need a 120/240 step up transformer between the SunnyIsland and the
> critical load panel to fully take advantage of the Sunnyboy array for
> battery charging, correct?.
>
> Kirk Herander
>
> VT Solar, LLC
>
> dba Vermont Solar Engineering
>
> NABCEP^TM Certified installer Charter Member
>
> NYSERDA-eligible Installer
>
> VT RE Incentive Program Partner
>
> 802.863.1202
>
> *From:*re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *David Katz
> *Sent:* Friday, October 05, 2012 2:11 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] AC coupling and Outback inverters
>
> Hi Kirk,
>
> All of the Outback inverters will work AC coupled (GT and FX) as will
> any bi-directional H-bridge type inverter. I have used old Trace SW’s,
> SunnyIsland, Apollo TSW, Magnum AE and now I am using an Outback Radian
> to do exactly what you are talking about. I have 6 kW of grid tie
> inverter and an additional 4kw of modules running through a Xantrex 600
> volt charge controller to the batteries that the Radian runs on. It all
> works flawless as long as you have a provision for protecting the
> batteries when the gid is down and the grid-tie PV system is making more
> power than the loads are using.
>
> If the customer has SMA inverters, I would recommend using a SunnyIsland
> because the battery control when the grid goes down is so elegant.
> Everything else is a bit of a kludge.
>
> David Katz
>
> CTO & Founder
>
> AEE Solar Inc
>
> P: 707 825-1200
>
> F: 707 825-1202
>
> dkatz at aeesolar.com <mailto:dkatz at aeesolar.com>
>
> www.aeesolar.com <http://www.aeesolar.com>
>
> *From:*re-wrenches-bounces at lists.re-wrenches.org
> <mailto:re-wrenches-bounces at lists.re-wrenches.org>
> [mailto:re-wrenches-bounces at lists.re-wrenches.org]
> <mailto:[mailto:re-wrenches-bounces at lists.re-wrenches.org]> *On Behalf
> Of *Kirk Herander
> *Sent:* Thursday, October 04, 2012 2:11 PM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] AC coupling and Outback inverters
>
> I have AC-coupled an Outback quad-stack with multiple SunnyBoy 6000US
> inverters and it’s been running fine for 4 years. I used the off-grid
> version of Outbacks.
>
> Now I have an application where a customer wants to add battery backup
> to an existing SunnyBoy 5000US system. And expand his array by a couple
> KW. So I’m thinking of using a GT Outback w/ batteries to handle the
> critical loads and feed the extra 2kw of PV (charging the batteries
> through an MX60) to the grid. And I’d like to AC-couple the SunnyBoy so
> the original 5 kw array can also charge the batteries, BUT I remember,
> at least I think so, that the GT inverter cannot be AC-coupled, only the
> off-grid version. Is this correct? Thanks.
>
> Kirk Herander
>
> VT Solar, LLC
>
> dba Vermont Solar Engineering
>
> NABCEP^TM Certified installer Charter Member
>
> NYSERDA-eligible Installer
>
> VT RE Incentive Program Partner
>
> 802.863.1202
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
More information about the RE-Wrenches
mailing list