690.13 specifically states that the grounded conductor shall NOT be
disconnected. All sections of Chapter III (Disconecting Means) of Article
690 specifically refers to the ungrounded conductor.

Jason Szumlanski
Fafco Solar


On Fri, Sep 14, 2012 at 7:39 PM, Bob Clark <bclark at solar-wind.us> wrote:

> Wrenches:****
>
> ** **
>
> A local utility person has suggested that both the positive and negative
> conductors from a solar array should be disconnected.****
>
> ** **
>
> Disconnect both or not?  2008 NEC supporting citation please.****
>
> ** **
>
> Thanks for your response.****
>
> ** **
>
> *Bob Clark*
>
> *SolarWind Energy Systems, LLC*
>
> *P.O. Box 1234*
>
> *Okanogan, WA 98840*
>
> *(509) 826-1259*
>
> * *
>
> *Although no trees were killed in the sending of this message, a large
> number of electrons were terribly inconvenienced.*
>
> [image: cid:822514723 at 19022009-0502]****
>
> * *
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20120915/4b22d65b/attachment.htm>


More information about the RE-Wrenches mailing list