Ray,
If golf cart batteries can't surge over 2000 amps, then it would seem
that the fuse in line with the QO can be deleted in some cases. Is
the 2000 A surge for one 6 volt battery or 2 in series?
Fuses can be put in the QO enclosure ahead of the loads and DC rated
Class T fuses can be bolted to battery terminals (code questionable,
but a good method for safety). In the old days we often had a DC
system with a few lights and maybe a Sunfrost. That way, if the
inverter went down, the home wouldn't be left in the dark. DC was
tricky code wise, but not impossible.
Thanks
Drake
At 08:03 PM 8/10/2012, you wrote:
>The QO breaker has an AIC of 5000 amps. The usual golf cart
>batteries have a short circuit current of about 2000 amps, so you
>could do a set of 4 golf cart batteries at 12v, without worrying
>about the extra fuse.
>Once again, if the system gets any bigger, they should just go to an
>inverter based design.
>Also, to be clear, I don't risk my license installing ATC fused
>systems on permanent structures. (strictly RVs, and portable set ups)
>As soon as I'm doing an install covered by the code, it's going to
>be code compliant, and it's going to be inverter based.
>Take a look at Midnite's Mini DC panel wired to Magnum's smallest
>inverter. You'd be surprised how cheap you can do a code compliant
>inverter based system, and how much money you can waste trying to do
>a code compliant DC only system.
>
>Ray Walters
>NABCEP certified since 2004
>
>On Aug 10, 2012, at 4:35 PM, Drake wrote:
>
> > I second using QO load centers. You will want to put a fuse,
> like an FRN-R, between the battery and the load center, as the QO
> breakers don't have a high AIC rating. 12 V systems can be wired as
> easily as a regular AC system.
> >
> >
> > At 05:05 PM 8/9/2012, you wrote:
> >> Hello,
> >>
> >> I've been looking at a lot of hunting shacks, fish houses and
> other 12V loads setups and was wondering how people go about
> setting these up? What are people using for load termination, fusing?
> >>
> >> I'd like to keep all disconnects and fusing in one "box".
> >>
> >> Jesse
> >>
> >> Sent from my iPhone
> >> _______________________________________________
> >> List sponsored by Home Power magazine
> >>
> >> List Address: RE-wrenches at lists.re-wrenches.org
> >>
> >> Options & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>
> >> List rules & etiquette:
> >> www.re-wrenches.org/etiquette.htm
> >>
> >> Check out participant bios:
> >> www.members.re-wrenches.org
> >
> > _______________________________________________
> > List sponsored by Home Power magazine
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Options & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out participant bios:
> > www.members.re-wrenches.org
> >
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list