[RE-wrenches] Deka AGM (was Small battery bank vs too large array:
Gary Willett
gary at icarussolarservices.com
Sat Aug 4 15:18:36 EDT 2012
Larry:
Are the problems you have encountered with the Deka/MK 12V AGMs also an
issue with the 8AGC2 6V AGM? Are the problems you're seeing with climate
controlled batteries, or with outside cabinet mounted batteries?
I have an application having I believe heat related failures with one
48V string of outside cabinet 8AGC2 batteries in an off-grid battery
based inverter/charger with generator charging (6kw LP generator).
Temperature compensated bulk charging of 60A DC is delivered to the bank
(0.3 x C20).
Gary
On 8/3/2012 5:03 PM, Larry Crutcher, Starlight Solar Power Systems wrote:
> Vince,
>
> I know of no such "vulnerability". In fact, an AGM can provide much
> more instant current than any flooded battery. Concorde (Lifeline,
> SunXtender, etc.) and Fullriver AGM's are very robust designs. On the
> other hand, Deka AGM's, specifically the 12 volt 8A8D, are not to be
> trusted at all. We have stopped selling all Deka/MK AGM's due to very
> high failure rate.
>
> One other point to consider, having 5 parallel strings of 12 volt
> batteries is generally asking for short battery life, especially with
> an AGM since you can not check the SG to be sure all are charged
> fully. Cells do not charge at the same rate and having parallel paths
> for current will leave some cells deficit charged. Having many
> parallel strings exacerbate this issue. If you do upgrade the bank,
> opt for lower voltage, higher capacity batteries.
>
> Larry Crutcher
> Starlight Solar Power Systems
> (928) 342-9103
> _
> _
>
> Just a word of caution on the AGM batteries. AGM's do have some
> vulnerabilities compared to deep cycle wet filled batteries. We had a
> bank of 20, 8A8D running a Buddhist Retreat compound and were unable
> to convince our clients that there were limitations to the amount of
> power that they could run at one time. They managed to overheat and
> destroy the whole bank of batteries we think by using too much power
> during a retreat camp. People had brought there own appliances to use
> at the camp and we still don't know what the total load was on the 4,
> Outback VFX 3648 inverters. I'm guessing it was up there close to the
> 14.4 kW limit of the Outback inverters. We also petitioned our client
> for a larger battery bank but they didn't think they would ever need
> that much power.
>
> --
>
> --
>
> *Vince McClellan
> Energy Design
> _www.solarenergydesign.com <http://www.solarenergydesign.com/>_
> p: 541.485.8122; f: 541.338.3168*
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20120804/3ee2b537/attachment.htm>
More information about the RE-Wrenches
mailing list