Mark, 
Good question... Whether or not to bond metal pieces in contact with other
"already bonded" metal pieces???
Unless i'm reading it wrong, if your T/F question is false, then you would
need to bond each/every L-foot that a mounting rail is bolted to. No?

benn
 
DayStar Renewable Energy Inc.
www.daystarsolar.ca  *  Ph: 780-906-7807
Construction Electrician Solar Photovoltaic Systems Certified
Certificate # 0007S
HAVE A SUNNY DAY





On 27/07/12 7:18 AM, "Drake" <drake.chamberlin at redwoodalliance.org> wrote:

>If the plates are bolted together,  then they are bonded to each other.
>
>At 01:33 AM 7/27/2012, you wrote:
>
>>Mark,
>>If you look at NEC 250.104(C), you'll find that you have to bond
>>structural
>>metal that is "likely to become energized". The phrase "likely to become
>>energized" is not defined, and is up to the AHJ. I would guess most AHJ's
>>would consider the second metal plate to already be bonded since it is
>>electrically continuous with the first metal plate, because they're
>>touching. I also doubt they would consider it "likely to become
>>energized"
>>because you bonded the first metal plate. Just my opinion.
>>
>>-Hans
>>
>>-----Original Message-----
>>From: re-wrenches-bounces at lists.re-wrenches.org
>>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mark Frye
>>Sent: Wednesday, July 25, 2012 7:29 PM
>>To: RE-wrenches
>>Subject: [RE-wrenches] Grounding - Exposed Metal Part
>>
>>A bare metal plate is connected to a conduit which serves as an equipment
>>ground. The plate is grounded and needs to be grounded because it could
>>become energized both by being contact with the conduit which could
>>become
>>energized and also by coming into contact with the current carrying
>>conductors themselves.
>>
>>A second bare metal plate touches the first plate but could not come into
>>contact with the current carrying conductors.
>>
>>True or false, the second plate does not have to be grounded (bonded to
>>the
>>first plate) because the first plate is already grounded and therefore
>>could
>>not cause the second plate to become energized?
>>
>>Any Code references to support your opinion?
>>
>>P.S. I believe: "false", the second plate must be bonded to the first
>>plate
>>because it may become energized by the first plate regardless of whether
>>or
>>not the first plate is actually grounded, but I can't find references in
>>the
>>Code to support this.
>>
>>Mark Frye
>>Berkeley Solar Electric Systems
>>_______________________________________________
>>List sponsored by Home Power magazine
>>
>>List Address: RE-wrenches at lists.re-wrenches.org
>>
>>Options & settings:
>>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive:
>>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>List rules & etiquette:
>>www.re-wrenches.org/etiquette.htm
>>
>>Check out participant bios:
>>www.members.re-wrenches.org
>>
>>
>>_______________________________________________
>>List sponsored by Home Power magazine
>>
>>List Address: RE-wrenches at lists.re-wrenches.org
>>
>>Options & settings:
>>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive: 
>>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>List rules & etiquette:
>>www.re-wrenches.org/etiquette.htm
>>
>>Check out participant bios:
>>www.members.re-wrenches.org
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>




More information about the RE-Wrenches mailing list