[RE-wrenches] Battery Experience

John DeBoever jdeboever at trojanbattery.com
Mon Jul 9 15:53:58 EDT 2012


Jason, Wrenches,

Thank you for your patience and positive statements on Trojan Battery Company. Last week was a busy and I was away from my desk most of the time with limited access to Internet.

Both the Premium "RE" versions L16RE-A and L16RE-B, and, the Signature  L16P & L16H are great deep-cycles lead acid batteries for solar applications. The key differences between them are:


ü  The grid is thicker for the Premium "RE" L16RE-A and L16RE-B, which effectively reinforces further the frame strength which results into a greater corrosion resistance;

ü  There is relatively more electrolyte in contact with the plates in the Premium "RE" L16RE-A and L16REB, which enhances the electrochemical reaction, particularly during PSOC;

ü  The rubber-based multi-rib geometry separator is approx. 30% thicker for the Premium "RE" L16RE-A and L16RE-B, which translates into a longer life of the separator. The thicker multi-ribs geometry keeps over time the acid channels open longer, promoting the flow of the electrolyte . As a result, the thicker separator is reducing the risk of stratification and enhancing electrochemical processing throughout the plates, resulting into longer continuous performance of the battery.

ü  In the approx. same form factor (except the height), this results into more lead per Ah capacity on the L16-RE units nameplate.


As a consequence, the cycling performances of the Premium "RE" is 1,600 cycles @ 50% DOD and 4,000 cycles @ 20% DOD. Respectively 1,200 cycles # 50% DOD, and, 3,000 cycles @ 20% DOD @ 20% DOD, for the L16-P & L16-H.

I hope this helps. Let me know if I can shed further light on other attributes of lead acid batteries.

Sunniest regards,

John

John F. DeBoever
Global Technical & Projects Director - Renewable Energy
Trojan Battery Company

12380 Clark Street
Santa Fe Springs, CA 90670
Tel: +1-562-236-3000 Ext. 3139
Cell: +1-845-514-7600 - NY office time zone: USA EST (GMT-5)
Skype: john.f.deboever
Fax: +1-562-236-3239
jdeboever at trojanbattery.com<mailto:jdeboever at trojanbattery.com>
www.trojanbattery.com<http://www.trojanbattery.com/>


From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jason Lerner
Sent: Sunday, July 01, 2012 11:26 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Battery Experience

I am back to using Trojan's after 12 years of trying others,  none seem to last as long for the L16's.  Could anybody explain the technical differences between the Trojan L16 and the L16RE-B's.  I have read all the brochures but would like to understand what is going on in there instead of getting the marketing of DuraGrid(tm), MaxGuard® XL separator and Alpha Plus.

Thanks very much,

Jason Lerner

Waldron Power and Light and Co.
On Jun 29, 2012, at 6:41 PM, Jonathan Hill wrote:


Over 20 years experience with them says you can't go wring with Trojan!
Jonathan Hill, senior system engineer and founder

Sierra Solar Systems
563C Idaho Maryland Road
Grass Valley, CA 95945
Celebrating our 32nd year in solar!
tech info and foreign orders:  (530) 273-6754
order line: (888) ON-SOLAR (US only)   FAX:  (530) 273-1760
e-mail:  <mailto:solarjon at sierrasolar.com>
world wide web:  <http://www.sierrasolar.com<http://www.sierrasolar.com/>>

Check out our 2 minute video at:
http://www.youtube.com/watch?v=WY-0UuabPEk<http://www.youtube.com/watch?v=WY-0UuabPEk>



On Jun 29, 2012, at 12:42 PM, Dave Palumbo wrote:


We have had less than stellar performance out of the Crown L-16's that we installed 4 to 5 years ago. Premature failure is my experience. About 60% of the cycle life compared to Trojan L-16's and also Surrette/Rolls. I've been using those since 1985.

Back to using Trojan. Specifically RE-B's either L-16, or T-105. And have used Trojan Industrial IND 13-6V on one system with good success with another set ordered.

Dave

From: re-wrenches-bounces at lists.re-wrenches.org<mailto:re-wrenches-bounces at lists.re-wrenches.org> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of SunHarvest
Sent: Friday, June 29, 2012 11:56 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Battery Experience

Just got talked into buying Crown (395Ah at 20Hr<mailto:395Ah at 20Hr>) as my local rep, "the battery expert", was persuasive in his testimony to their reliability. Should've consulted wrenches first.

Should I be worried??

Eric Stikes
SunHarvest Solar
+1 (530) 798 - 3738
www.harvesthesun.com<http://www.harvesthesun.com/>
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org/>

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>



This e-mail message and any attachments that accompany it may contain 
information that is confidential, privileged, or protected from disclosure.  
It is intended solely for the use of the individual(s) to whom it was intended 
to be addressed. If you have received this e-mail by mistake, or you are not 
the intended recipient, any reading, disclosure, copying or other use of this 
communication is strictly prohibited.  If you have received this communication 
in error, please immediately advise the sender at their phone number listed 
above, or by electronic mail, and also permanently delete the original and all 
copies of this e-mail and any attachments from all locations. Thank you.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20120709/f34e61f0/attachment.htm>


More information about the RE-Wrenches mailing list