Kent,
I haven't any direct experience with the smart meters tripping inverters,
but the issue of SCRs and generators is well known. I suspect you
understand the problem, but to recap it, the problem revolves around the
way SCRs make a sine wave.
A motor driven generator controls the alternator output by increasing or
decreasing the DC excitation level. It does that by sensing the "zero
crossing", or point in the sine wave at which the voltage is zero. This
happens 120 times a second on a 60Hz system.
When the source of the electricity is electronic, the waveform will
sometimes be messy around the zero crossing. That gives the voltage control
circuit problems to detect the zero crossing We see this a lot when trying
to drive a UPS from a generator, it can drive the generator crazy.

I suspect your problem is the same. The SCR in the meter disturbs the
waveform and the inverter thinks it is a faulty waveform.
 I would try a low pass filter between the meter and the inverter. A
properly sized capacitor ought to remove any noise above 60hz and present a
clean waveform to the inverter.


On Sun, Jul 8, 2012 at 7:06 PM, Kent Osterberg <kent at coveoregon.com> wrote:

> Wrenches,
>
> There weren't very many replies to my question about grid-connected
> inverter compatibility with utility remote meter reading systems so I'll
> explain my recent experience with hope that this information may be of
> assistance sometime.
>
> Last fall I installed an Ephase system for a customer. Soon after it was
> on line he complained that the inverters were dropping off line frequently.
> Since we had a lot of cloudy weather in northeast Oregon all winter, it
> wasn't easy to see what was going on. In the spring we had some clear days
> and noticed that the inverters were dropping off line several times a day
> at exactly the same time every day. It didn't take very long for our
> suspicion to turn to the utilities new remote meter reading equipment.
> Because our weather has been so cloudy it took a while to find clear days
> where the utility could provide assistance. But with their help by reading
> the meter on demand and temporarily disabling the meter communications we
> were able to finally prove the remote meter reading system is tripping the
> inverters offline for five minutes every time the meter sends a data packet.
>
> Recently the remote meter reading system has expanded to more areas so we
> have now observed this problem with both Enphase M190 and M215 inverters.
> The system we've observed that is in town is seeing many more dropouts, so
> we think every kWh meter on the same service transformer and maybe some
> beyond it are causing trouble too.
>
> The remote meter reading equipment is made by Aclara and uses their TWACS
> technology. This isn't new technology and with more remote meter reading
> systems going in all the time there will be more occurrences of
> incompatibility. Certainly more between Enphase and TWACS. And possibly
> more between other inverters and other communications systems.
>
> At present I'm really dissatisfied with Enphase's support on this issue.
> All they've done is point out that only a few systems have been affected
> and put us in the position of telling customers that they'll just have to
> live with the lost production time. Until Enphase comes up with a fix, I
> won't install any more Enphase inverters.
>
> --
> Kent Osterberg
> Blue Mountain Solar, Inc.
> www.bluemountainsolar.com
> t: 541-568-4882
>
> ______________________________**_________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.**org<RE-wrenches at lists.re-wrenches.org>
>
> Options & settings:
> http://lists.re-wrenches.org/**options.cgi/re-wrenches-re-**wrenches.org<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>
> List-Archive: http://lists.re-wrenches.org/**pipermail/re-wrenches-re-**
> wrenches.org<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.**htm<http://www.re-wrenches.org/etiquette.htm>
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20120708/db7318d2/attachment.htm>


More information about the RE-Wrenches mailing list