[RE-wrenches] Independent vs common trip two-pole breakers
August Goers
august at luminalt.com
Fri May 11 18:52:25 EDT 2012
Hi Wrenches,
I'm doing a little circuit breaker homework and have been trying to figure
out if standard residential two-pole breakers for the inverter need to be
independent or common trip type. For example, Eaton Cutler-Hammer make
quadplex independent trip type and common trip type. My understanding is
that manual operation of either of these types must be done with both
two-poles. However, the independent trip type will trip one side of the
circuit without tripping the other. Incidentally, the rejection tab feature
(which prevents the breaker from being installed on non-notched type
busbars) seems to be more prevalent on the common trip models. Anyone a
breaker guru who can explain why one might one or the other?
Thanks,
August
August Goers
Luminalt Energy Corporation
1320 Potrero Avenue
San Francisco, CA 94110
o: 415.641.4000
august at luminalt.com