Colleagues:

I might caution against using the HBX mode for two reasons:

1. The batteries will "wear out" in proportion to the number of cycles.  If 
you don't need to cycle then I recommend you don't.

2. HBX can be a very inefficient mode.  If you HBX cycle frequently then 
you are double-converting your power:  Converting AC to DC to charge 
batteries and then converting DC to AC to power loads.

William Miller


At 08:43 PM 5/4/2012, david at wind-sun.com wrote:

>Eventually all batteries wear out but that is no reason to give up on them 
>because the grid is coming in.  It sounds like he simply wants to continue 
>using his off-grid system and let the grid take over if the modules can't 
>keep up with the demand.  If you're using outback inverters simply program 
>them for HBX mode.
>
>
>David Lauzon
>Northern Arizona Wind and Sun Phone-928-526-8017 / 800-383-0195 
>Fax-928-527-0729
>Website-<http://www.solar-electric.com>http://www.solar-electric.com