1 - What is the AC output rating of the PV inverter?
2 - What is the size of the feeder conductors?
3 - Does the sub panel at the garage have a main breaker of it's own?
4 - Does your AHJ or utility require anAC disconnect or not?

Mark Frye
Berkeley Solar Electric Systems



On 4/11/2012 7:09 AM, Aladdin Solar wrote:
> Wrenches:
> There's probably an obvious answer but please help me think this 
> through. Here's the situation--comes up all the time: The PV array and 
> grid-tied inverter will be located on a detached building (garage or 
> pole barn, etc.). The existing power to the building is a 240V 60A 
> subpanel connected to the main panelboard at the house or main 
> building via buried cable. If we obey buss bar loading and wire 
> sizing, etc, is there any reason why we can't or shouldn't install the 
> small grid tied PV system and tie it into the garage subpanel instead 
> of trenching new lines back to the house and hit the main panel 
> there? One hitch I see is that if we want a PV system AC disconnect 
> near the main meter, the whole garage would end up on that. Have 
> I overlooked an NEC or inverter requirement?
> Thanks for your comments.
> Charlie Pickard
> Aladdin Solar
>
>
> __________ Information from ESET NOD32 Antivirus, version of virus 
> signature database 7045 (20120411) __________
>
> The message was checked by ESET NOD32 Antivirus.
>
> http://www.eset.com
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options&  settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules&  etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20120411/cac56c0a/attachment.htm>


More information about the RE-Wrenches mailing list