Hi Kris,

 

A solution to try would be to add a motor run capacitor across the line
at the boiler.  10uF-20uf range may improve the crossover distortion
enough to allow the boiler ignitor to operate properly. Start with 10uF.


 

Regards,

Brian

 

Brian Faley

Chief Engineer

Magnum Energy Inc.

2211 West Casino Rd

Everett, WA 98204

Ph 425-353-8833

www.magnumenergy.com

 

 

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of
Kristopher Schmid
Sent: Monday, March 26, 2012 11:51 AM
To: RE-wrenches
Subject: [RE-wrenches] Wood boiler ignition issue

 

Esteemed wrenches,

I am assisting in troubleshooting a stand alone system with three
stacked Magnum 4448 PAE inverters.  The electric ignition of LP for the
wood boiler will not fire from inverter power.  As soon as we fire up
the generator, the boiler ignites.  Has anyone seen this before?  Is
there a solution?  The boiler is a Central Boiler E-Classic 2400.