[RE-wrenches] Absolyte recovery

mac Lewis maclewis1 at gmail.com
Fri Feb 17 10:08:48 EST 2012


Hi Chris,

I suspect that the charger in the Apollo Inverter/Charger is undersized,
especially since all of the loads are -48V.  Conversely, the array is very
oversized and the controllers float most of the time.  The charge
controllers were working fine last I checked.  It's difficult to access the
site right now, it includes a 30 mile snow mobile ride.  We intended to put
a comprehensive remote monitoring system but it didn't get put in before
the snow came.  I want to get up there and help the system limp along until
snow melt when we can do a thorough assessment.
The generator guy went up there and someone had pulled the stop switch on
the genset.  The battery voltage was around 5V on a 48V bank.  Yikes!

  Thanks for the contact info.

On Thu, Feb 16, 2012 at 2:13 PM, Chris <chris at solarwindworks.com> wrote:

> Hi Mac,****
>
> We had a cell failure on an Absolyte system we inherited and contacted;***
> *
>
> Jeff Lambert
> Product Support and Warranty
> East Penn Mfg. Co., Inc. - Unigy Battery Division ****
>
> ( Office: (610) 682 – 6361 ext. 2848   | *È*Cell: (484) 955 – 2899  |  ÇPage:
> 888-797-8039  (If no answer on Cell)  |  * Email:
> jlambert at eastpennunigy.com****
>
> Jeff was very helpful.****
>
> I do wonder if your charge controllers are getting the array power out to
> the battery bank, was there any damage to them too? Is the Apollo 4048
> inverter/charger doing its job, is it undersized for the size of battery
> bank?****
>
> ** **
>
> Sincerely,
>
> Chris Worcester****
>
> Solar Wind Works
> NABCEP Certified PV Installer
> Phone: 530-582-4503
> Fax: 530-582-4603
> www.solarwindworks.com
> chris at solarwindworks.com
> "Proven Energy Solutions"****
>
> ** **
>
> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *mac Lewis
> *Sent:* Thursday, February 16, 2012 12:43 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Absolyte recovery****
>
> ** **
>
>  Wrenches,****
>
> ** **
>
> We have inherited a Telecomm system in which the batteries have had a very
> hard life.  A lighting strike knocked the system off line for about 5
> months, and ground fault dragged the batteries way down about a month ago.
>  Now, we are seeing about 10h of generator run time/day indicating to me
> that the batteries are not holding voltage at all.****
>
> ** **
>
>   I am uncertain of the exact specs at this moment, but it is a 24
> Absolyte IIP batteries (5 years old), with a 5 kW array, two Apollo T80HV
> charge controllers and an Apollo 4048 inverter charger.****
>
> ** **
>
> I don't have experience with these batteries.  Is there any way to try to
> recover these batteries?  Any good contacts with GNB would be useful.****
>
> ** **
>
> Thanks
> ****
>
> ** **
>
> ** **
>
> Wrenches,****
>
> ** **
>
> We have inherited a Telecomm system in which the batteries have had a very
> hard life.
> ****
>
> ** **
>
> -- ****
>
> ** **
>
> ** **
>
> ** **
>
> Mac Lewis**
>
> "Yo solo sé que no sé nada." *-Sócrates*****
>
> ** **
>
>
>
> ****
>
> ** **
>
> -- ****
>
> ** **
>
> ** **
>
> ** **
>
> Mac Lewis**
>
> "Yo solo sé que no sé nada." *-Sócrates***
>
> ** **
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 



Mac Lewis

*

"Yo solo sé que no sé nada." -Sócrates
*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20120217/5a9fe6f8/attachment.htm>


More information about the RE-Wrenches mailing list