[RE-wrenches] Carling C Series Breakers (was Outback Breaker problem)

Ray Walters ray at solarray.com
Fri Jan 6 13:47:12 EST 2012


Hi Wrenches;

Here's an update on the breaker problem.  Midnite is getting their 
breakers changed over to the sturdier posts.  I had less trouble with 
the Epanel, than working backwards in the super deep Outback box, 
anyway.  Hopefully Outback will follow suit now?  As I stated before, I 
would pay a bit more for a breaker that didn't snap off in the field, as 
its way cheaper than a return trip on an off grid project.  Its always 
nice to feel like we wrenches in the field are being listened to.  We're 
really trying to make this better and safer for everyone involved.

Ray Walters

-----Original Message-----
Subject: Carling C Series Breakers

An Engineering Change Order has been initiated by Carling to change your 
terminations to 1/4 20 Welded Studs as we discussed yesterday. New part 
numbers will be issued.