[RE-wrenches] Pole Mount PVC
North Texas Renewable Energy
ntrei at 1scom.net
Sat Dec 31 10:01:53 EST 2011
Drake- on the tracker installs we've done, the method you describe is standard procedure. the exception is that on our very first we used RMC wrapped in a continuous layer of anti-corrosion tape to keep the wet concrete from attacking the zink coating.
On all jobs since then we have used only rigid NM stubbed up to just inches above the surface of the finished pier. Then we transisitioned to EMT, offset and bolted firmly to the steel pipes.
This process has passed muster when buried conduit penetrated a concrete foundation into the new equipment room. A exterior pier should be no different from a concrete foundation. Most any commercial electrical contractor in your area should be able to detail the process that works in that jurisdiction.
Jim Duncan
North Texas Renewable Energy
817.917.0527
ntrei at 1scom.net
TECL 27398
NABCEP Solar PV
Certified 031310-57
www.ntrei.com
----- Original Message -----
From: Drake
To: re-wrenches at lists.re-wrenches.org
Sent: Saturday, December 31, 2011 8:38 AM
Subject: [RE-wrenches] Pole Mount PVC
Hello Wrenches,
With pole mount systems, It looks cleaner and is safer to run the PVC conduit down the pole into the concrete, and use a 90 degree elbow to come out through the side of the anchor underground. This way, the pipe is protected from mechanical damage, and there is nothing to trip over when adjusting the array for seasonal tilt.
I was told that some building departments will not allow this. Has anyone had a problem with using this method, either technical or legal? How do you like to route your conduits?
Thank you,
Drake
Drake Chamberlin
ATHENS ELECTRIC LLC
OH License 44810
CO license 3773
NABCEP Certified PV
------------------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20111231/69bc3be8/attachment-0001.htm>
More information about the RE-Wrenches
mailing list