[RE-wrenches] GEC and EGC Advice
JRQ
quackkcauq at yahoo.com
Tue Dec 6 12:13:15 EST 2011
I'd avoid using the metal conduit as the only bond in your equipment grounding from the roof down to other equipment. If the GEC is bonded to the rest of the equipment grounding system at a point on the ground, then of course it can double as the EGC. Otherwise, if you don't want to use a separate EGC conductor, better to split-bolt or splice by another means from the GEC once you're on the ground and run an EGC back to busbar in the equipment grounding system.
Jeffrey Quackenbush
NABCEP-certified PV installer
Ninja Solar
________________________________
From: Allen Frishman <amfrish at aeonsolar.com>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Tuesday, December 6, 2011 1:59 PM
Subject: [RE-wrenches] GEC and EGC Advice
Fellow Wrenchers,
I know this topic has come up before and I have a understanding but I am looking for best practices advice.
When installing a 50KW or larger 3 phase 208V (WYE Service) Inverter on a roof do you run your Grounding Electrode Conductor in a separate conduit from the 3 hots, and the Equipment Grounding Conductor or do you run it all in the same conduit together.
My thought is to run it all in the same conduit and utilize the metalic conduit as the Equipment Ground instead of running a actual conductor for the EGC.
All feedback is appreciated.
Al Frishman
AeonSolar
(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20111206/fa5ce546/attachment-0001.htm>
More information about the RE-Wrenches
mailing list