[RE-wrenches] Small Off-Grid Inverter Recommendation
bob ellison
reellison at gmail.com
Fri Nov 11 12:20:07 EST 2011
If you need a charger capability, look at the magnum MMS1012. Up to a 50 amp
charger and it's a sinewave, don't bother with the modifieds. Sleep mode can
go down to 5 watts I think.
The Morningstar mppt is a good small controller that works well
Later,
Bob
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jeff Irish
Sent: Friday, November 11, 2011 10:46 AM
To: RE-wrenches
Subject: [RE-wrenches] Small Off-Grid Inverter Recommendation
Any recommendations from those of you with extensive off grid experience for
a small inverter, sine wave, 500-1000 watt range 120 vac output, 12 or 24
VDC nominal input? I'm looking for something with low standby losses when
there are no loads, and high reliability. Thanks!
Jeff Irish, PE
President
Hudson Valley Clean Energy, Inc.
and Adirondack Solar
13 Hook Road
Rhinebeck, NY 12572
T.845.876.3767x110
F.845.876.3912
jeff at hvce.com
Renewable Energy Systems
Solar, Wind, Geothermal
NYSERDA Eligible PV Installer
NABCEP Certified PV Installer
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20111111/bdbdb731/attachment-0001.htm>
More information about the RE-Wrenches
mailing list