[RE-wrenches] cable spacing in trenches
bob ellison
reellison at gmail.com
Thu Nov 3 18:19:29 EDT 2011
What are you running for combiner boxes and wire to run at 1000 volts?
Seems that I remember that fuses are only good for 600 volts and most boxes the same limit?
What are you using?
Just wondering,
Bob Ellison
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jerry Caldwell
Sent: Thursday, November 03, 2011 5:42 PM
To: RE-wrenches
Subject: [RE-wrenches] cable spacing in trenches
Can anyone direct me to the NEC article that stipulates how many inches of separation must be between cables operating at different voltages?
I have a project with PV combiner box home runs at 1,000 volts DC in the same trench with 12.47 kV cables. Table 300.5 shows minimum cover requirements for direct burial cables, but this is the distance beneath grade the cables must be. Is there anywhere in the code that calls for a minimum separation distance between cables at different voltages?
Thanks,
Jerry Caldwell
_____
From: Marco Mangelsdorf <marco at pvthawaii.com>
To: 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
Sent: Thursday, November 3, 2011 2:27 PM
Subject: [RE-wrenches] under performing Enphase inverters
For the first time, several weeks ago, after 40-50 Enphase installs, we’ve come across at least two M210s that we putting out consistently lower outputs than their immediate neighbors.
We replaced the two mods first, which made no difference. Then, in consultation with Enphase, replaced the M210s. After replacing them, the power output was as it should be.
Now I’ve got another suspect system with several underperforming mods out of (36).
Has anyone else had this experience?
Thanks,
marco
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20111103/880cf122/attachment-0001.htm>
More information about the RE-Wrenches
mailing list