[RE-wrenches] Generator-Transfer Switch-Solar

Jason Szumlanski Jason at fafcosolar.com
Wed Jul 20 15:18:20 EDT 2011


Keith,

 

I think if you search the archives you will find a bunch of information
on this subject. The general consensus, I believe, was to not try to
back feed a generator. Make your point of interconnection ahead of the
generator transfer switch. Often this means a supply side connection is
easier if the home is already wired for a whole house generator. 

 

I seriously doubt you will have a big impact on fuel consumption, even
if you are able to run the PV system and generator in parallel
operation. The PV to generator size ratio would need to be sufficiently
small for this to work. You certainly don't want to attempt to operate a
10kW inverter output in parallel with a 5kW generator, for example. If I
understand it right, the generator would overspeed and the inverter(s)
would lose sync.

 

Anyway, if you don't want to replace expensive generator control boards
if it doesn't work, just isolate the systems altogether. I've never
tried it... too chicken, or maybe too smart... J

 

Jason Szumlanski

Fafco Solar 

 

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Keith
Cronin
Sent: Wednesday, July 20, 2011 3:05 PM
To: RE-Wrenches
Subject: [RE-wrenches] Generator-Transfer Switch-Solar

 

Wrenches

 

With the advent of micros on the scene and the potential for using a
generator on an on-grid property, are any of you using a transfer switch
to isolate the genny and use the PV to feed the genny to reduce fuel
consumption?

 

Are there issues with frequency and voltage?

 

How are the utilities looking at these types of installations?
Favorable?

 

Would you use 2 transfer switches- one ahead of the other- to completely
isolate the property or circuit panel to ensure there is no chance of a
backfeed?

 

Is it just better to keep things isolated as two separate systems?

 

Regards,

Keith

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20110720/6a923a6b/attachment-0001.htm>


More information about the RE-Wrenches mailing list