[RE-wrenches] 120 volt inverter to 480 3 phase

Darryl Thayer daryl_solar at yahoo.com
Thu May 12 19:38:55 EDT 2011


Most facilities that have 480 volt service have either 120/208 or 120/240 volt 
transformers to provide plug loads.  You connect to one of these transformers.  
If in the rare case you do not have any plug load transformer you provide a 
120-480 or 120-277 volt transformer. 

If your service is   277/480 V  and you have 120-208 plug load transformer 
servicing the building, and your critical loads are 120 208 three phase, you can 
service these loads with the Three phase 120 volt outbacks set to three phase.  
If the load is about 10kW or larger you will need the new outback units (8kW in 
a box)  


DT 




________________________________
From: Kristopher Schmid <solman at legacysolar.com>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Thu, May 12, 2011 6:20:02 PM
Subject: [RE-wrenches] 120 volt inverter to 480 3 phase

Esteemed wrenches,

One of my students asked me today how you would (or if you could) connect a 120 
volt outback inverter to a 277/480 volt 3 phase service.  I said those three 
little words that men find so hard to say, "I don't know".  Help, please.

-- 
Thanks,
Kris Schmid

Legacy Solar, LLC
864 Clam Falls Trail
Frederic, WI 54837
715-653-4295
www.legacysolar.com
solman at legacysolar.com