[RE-wrenches] NABCEP Test
Andrew Truitt
atruitt at gmail.com
Fri Apr 1 12:24:18 EDT 2011
>From Ezra:
Larry,
NABCEP provides test takers with a passing score and a partial breakdown of
their score by exam blueprint area. It is always a bit confusing because we
report only on those exam blueprint areas where there are sufficient number
of questions for the information provided to be relevant. For example
informing a candidate that they scored 50% in an area where there were only
two questions provided little useful information but informing the same
candidate that they scored 50% on an area where there are ten questions
clearly informs them that this is an area where further study is required.
We do not provide candidates with individual questions they missed as this
would have a strong negative impact on the security of the exam. If we
informed candidates on individual questions we would have to retire each
exam question we did so with which would put a huge burden of developing new
questions on our volunteer exam committee. It would also but a burden on the
exam itself as we would be continually retiring statically field proven
questions.
I know it is disappointing to candidates to not see the questions they
missed, and if I was a candidate I'd likely be frustrated as well. I also
know that it is simply not practical to do so and that our procedures are in
accordance to established and recognized testing protocols.
Sincerely,
Ezra Auerbach
Executive Director
For a brighter energy future,
Andrew Truitt
Principal
Truitt Renewable Energy Consulting
NABCEP Certified PV Installerâ„¢ (ID# 032407-66)
<%28202%29%20486-7507>(202) 486-7507
http://www.linkedin.com/pub/andrew-truitt/8/622/713
[image: 24 copy.jpg]
"Don't get me wrong: I love nuclear energy! It's just that I prefer fusion
to fission. And it just so happens that there's an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it's wireless!"
~William McDonough
On Fri, Apr 1, 2011 at 6:57 AM, <wirewiz at gmail.com> wrote:
> Ezra,
>
> Do you follow guidelines as to the "rights and responsibilities" of test
> takers. Do test takers have a right to see the questions they got wrong?
>
> Larry Liesner
> Wirewiz
> Westport, CT
> Phone: 203-644-2404
> Fax: 203-557-0556
> wirewiz at gmail.com
> www.wire-wiz.com
>
>
>
> On Apr 1, 2011, at 1:14 AM, Andrew Truitt wrote:
>
>
> This is what Ezra Auerbach, Executive Director of NABCEP, has to say on the
> matter:
>
>
> Hi Nick et al,
>
> A couple of clarifications. It has always taken a month or more for NABCEP
> to issue score reports on installer exams. Entry Level results tend to be
> quicker and this might be a source for confusion.
>
> I'll do my best to explain the passing score process. There is no set
> percentage or number of correct answers. Each exam is different from the
> last and is a mix of "field proven" and new questions. We use professional
> psychometricians for exam design and evaluation. They work with the subject
> matter experts on the exam committee. After each exam they all meet and
> review the performance of the exam with particular focus on new questions.
> Sometimes a question performs poorly which is to say a very high percentage
> of candidates who otherwise did well got it wrong. This sort of item is
> flagged for committee review. They sometimes decide it was a poor question
> and choose not to score it which is one reason for variance between exams.
>
> The Psychometrician uses a well established and accepted statistical review
> protocol that is designed to ensure consistency across multiple exam
> administrations. They then present their professional recommendations to the
> Board for their acceptance. This again is standard procedure for "Board"
> exams.
>
> In summary NABCEP follows well established internationally recognized
> scoring protocols that are fully psychometrically defensible which is part
> of the reason our PV Installer Certification has received accreditation by
> ANSI to their 17024 standard for personnel certification. We remain the only
> PV credentialing body in North America to have been accredited to this
> standard.
>
> I hope this helps. To each and every Wrench who is waiting for their exam
> results-I hope you passed.
>
> Regards,
>
> Ezra
>
>
> Ezra Auerbach
> Executive Director
> NABCEP"
>
>
>
> For a brighter energy future,
>
> Andrew Truitt
> Principal
> Truitt Renewable Energy Consulting
> NABCEP Certified PV Installerâ„¢ (ID# 032407-66)
> <%28202%29%20486-7507>(202) 486-7507
> http://www.linkedin.com/pub/andrew-truitt/8/622/713
>
> <24 copy.jpg>
>
> "Don't get me wrong: I love nuclear energy! It's just that I prefer fusion
> to fission. And it just so happens that there's an enormous fusion reactor
> safely banked a few million miles from us. It delivers more than we could
> ever use in just about 8 minutes. And it's wireless!"
>
> ~William McDonough
>
>
>
>
> On Thu, Mar 31, 2011 at 11:35 AM, <wirewiz at gmail.com> wrote:
>
>> Nick,
>>
>> The passing grade is 70, they don't change that. I think they just wan't
>> to see if any one question was consistently answered wrong and so maybe
>> there was a problem with the question and they may decide that everyone gets
>> that question right. I would guess that rarely happens.
>>
>> As far as the six weeks to wait for pass/fail notification, they keep you
>> hangin!
>>
>> They notify you by snail mail, not email. Hint: if the plain brown
>> envelope says "do not bend" on it, pop the champagne, you passed.
>>
>> Larry Liesner
>> Wirewiz
>> Westport, CT
>> Phone: 203-644-2404
>> Fax: 203-557-0556
>> wirewiz at gmail.com
>> www.wire-wiz.com
>>
>>
>>
>> On Mar 31, 2011, at 12:37 PM, Jamie Johnson wrote:
>>
>> That sounds about right, a NABCEP board member told me they meet and
>> vote on the difficulty of each question.
>>
>> So 5-7 weeks of wondering if you have what it takes to pass.........
>>
>> When you get the email notification it will say "congratulations" or
>> something to that effect in the subject line when you pass, not sure what it
>> says if you don't.
>>
>>
>> Jamie Johnson
>> NABCEP Certified Solar PV Installer
>> NABCEP Certified PV Technical Sales Professional
>>
>> General Manager
>> SOLAR POWER ELECTRIC
>> (941) 380 - 0098
>> EC13001765
>> www.SPEFL.com <http://www.spefl.com/>
>>
>> Sent from my iPhone
>>
>> On Mar 31, 2011, at 11:42 AM, Nick Soleil <nicksoleilsolar at yahoo.com>
>> wrote:
>>
>> Hi wrenches:
>> I sat for the NABCEP exam last weekend, and was surprised yesterday to
>> hear that we will not receive the exam results for another month! I had
>> heard that it only took a week. What was your experience. Also, the e-mail
>> yesterday said that the Board has to decide what grade will be a passing
>> grade? Can that be true? Does the grade get set to control the number who
>> pass or fail? That doesn't seem right.
>>
>> Nick Soleil
>> Project Manager
>> Advanced Alternative Energy Solutions, LLC
>> PO Box 657
>> Petaluma, CA 94953
>> Cell: 707-321-2937
>> Office: 707-789-9537
>> Fax: 707-769-9037
>>
>>
>> ------------------------------
>> *From:* Hans Frederickson <hans at fredelectric.com>
>> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> *Sent:* Thu, March 31, 2011 8:15:19 AM
>> *Subject:* Re: [RE-wrenches] Expansion joints
>>
>> We used an OZ-Gedney expansion coupling for 1-1/4" EMT on a recent job.
>> The part # is TX-125 for 1-1/4", and it would be TX-150 for 1-1/2". It is
>> the same as the OZ-Gedney AX expansion coupling for rigid conduit, but
>> uses a rigid nipple and EMT connectors to adapt to EMT. The assembly is UL
>> listed.
>>
>> -Hans
>>
>>
>> ------------------------------
>> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
>> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Erika Weliczko
>> *Sent:* Wednesday, March 30, 2011 5:54 PM
>> *To:* 'RE-wrenches'
>> *Subject:* Re: [RE-wrenches] Expansion joints
>>
>> I recently used a Hubbell Killark product for rigid/IMC and was *not*happy with how the threads of the coupling engaged in factory conduit
>> threads.
>>
>>
>> Crousehinds XJG-EMT series is intended for EMT. And is described as being
>> used indoors or outdoors. The EMT couplings mostly seem to be compression.
>>
>>
>>
>> REpower SOLUTIONS
>>
>> <http://www.repowersolutions.com/>www.repowersolutions.com
>>
>> P: 216.268.2275
>>
>> C: 216.402.4458
>>
>>
>> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
>> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Jamie Johnson
>> *Sent:* Tuesday, March 29, 2011 2:33 PM
>> *To:* RE-wrenches
>> *Subject:* [SPAM] Re: [RE-wrenches] Expansion joints
>>
>>
>> Peter,
>>
>>
>> Cooper makes one for 1.5" emt, not sure if it is rated for wet locations
>> or not.
>>
>>
>> part #XJG54 EMT, it allows for up to 4" max of conduit movement.
>>
>>
>> Jamie Johnson
>>
>> NABCEP Certified PV Technical Sales Professional
>>
>> NABCEP Certified Solar PV Installer
>>
>>
>> General Manager
>>
>> SOLAR POWER ELECTRIC
>>
>>
>>
>> **
>>
>>
>>
>> -------- Original Message --------
>> Subject: [RE-wrenches] Expansion joints
>> From: "Peter Parrish" < <http://peter.parrish@calsolareng.com%3e/>
>> peter.parrish at calsolareng.com>;
>> Date: Tue, March 29, 2011 1:04 pm
>> To: "'RE-wrenches'" < <re-wrenches at lists.re-wrenches.org>
>> re-wrenches at lists.re-wrenches.org>
>>
>> Does anyone have information (manu and part number) for expansion joints
>> for
>> 1-1/2 EMT? I have also heard that many EJs are designed for rigid conduit
>> (RMC) and may not be directly applicable to EMT.
>>
>> - Peter
>>
>> Peter T. Parrish, Ph.D., President
>> California Solar Engineering, Inc.
>> 820 Cynthia Ave., Los Angeles, CA 90065
>> CA Lic. 854779, NABCEP Cert. 031806-26
>> <http://peter.parrish@calsolareng.com/>peter.parrish at calsolareng.com
>> Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: <RE-wrenches at lists.re-wrenches.org>
>> RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> <http://www.re-wrenches.org/etiquette.htm>
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> <http://www.members.re-wrenches.org/>www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: <RE-wrenches at lists.re-wrenches.org>
>> RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20110401/26cba1cb/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 24 copy.jpg
Type: image/jpeg
Size: 35142 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20110401/26cba1cb/attachment-0001.jpg>
More information about the RE-Wrenches
mailing list