David,

This is for grid-tied carport structures which may be installed in several
locations on the East Coast where the minimum temperature varies from 5
degrees F to -20 degrees F and I would like to maintain one standard system
for each situation.  Three strings of 12 modules fit the carport exactly and
work well to 5 degrees but then the cold puts the voltage over 600.  I could
do 4 strings of 9 but then the high temperatures in summer cause the
inverters to drop out due to low voltage.

I could do three strings of 11 and have 3 dummy panels but would like to
avoid this kluge.

Thanks!

Lee

On Mon, Jan 10, 2011 at 5:44 PM, David Katz <dkatz at asis.com> wrote:

>  Lee,
> We never had enough interest to warrant getting a UL listing on the
> product. Is it for grid-tie or off-grid?
> David
>
>  David Katz
>
> Founder & CTO
>
> AEE Solar
>
> T(707) 825-1200
>
> C(831) 325-9582
>
> F(707) 825-1202
>
> dkatz at aeesolar.com <david at aeesolar.com>
>
> www.aeesolar.com
>
>
>
> DISCLAIMER:
> This communication, along with any documents, files or attachments, is
> intended for the use of only the addressee and contains privileged and
> confidential information. If you are not the intended recipient, you are
> hereby notified that any dissemination, distribution or copying of any
> information contained in or attached to this communication is strictly
> prohibited.  If you have received this message in error, please notify the
> sender immediately by e-mail reply and destroy the original communication
> and its attachments without reading, printing or saving in any manner.
>
>
>
> Try our new Online Store. Purchase product, check availability, review your
> account- fast and easy!
>
> [image: Signature]
>
> [image: Signature]
>
> On 1/10/2011 1:07 PM, Allan Sindelar wrote:
>
> Lee,
> I think Dave Katz at AEE had a solution, although I don't remember the
> details. You might contact him.
>
>  *Allan** Sindelar*
> Allan at positiveenergysolar.com
> NABCEP Certified Photovoltaic Installer
> EE98J Journeyman Electrician
> *Positive Energy, Inc.*
> 3201 Calle Marie
> Santa Fe, New Mexico 87507
> *505 424-1112*
> www.positiveenergysolar.com
>
> On 1/10/2011 12:45 PM, Lee Bristol wrote:
>
> Wrenches,
>
> Does anyone know of a UL Listed low temperature, over-voltage bypass
> device like the dis-continued Apollo Solar product?  I need to knock
> out or bypass one module of a string when the temperature gets below 5
> degrees F.  The Apollo product was appropriate but is no longer
> available.
>
> Thanks!
>
> Lee
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Lee Bristol
NABCEP Certified Solar Designer/Installer

Co-Founder & Commercial Channel Manager
Standard Solar, Inc.
1355 Piccard Drive, #300
Rockville, MD 20850
(301) 944-5105
(240) 479-1510 (c)
www.standardsolar.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20110111/58b7f6ca/attachment-0001.htm>


More information about the RE-Wrenches mailing list