Fellow Wrenches,
I would welcome some feedback on this one:
I may be "adopting" an eleven year old, Y2K, grid tie with battery back-up
system. It consists of 12 - Astro-Power 120 modules, installed in 2000, 12 -
Evergreen EC-110 modules installed in 2004, only one MX60, which controls BOTH
sub-arrays, one SW4048 in SELL mode through a dedicated load sub-panel.
Existing, seven year old battery is shot (8-Trojan L-16). Initial bank of
unknown batteries was replaced after only four years.
Recent long, nearby, utility outages have the client requesting a proposal to
include a new back-up generator and to restore the system selling to the grid.
Client may decide go straight grid tie to eliminate the batteries. They have
found the maintenance to be a hassle.
My thoughts so far:
1)To take advantage of most of the existing hardware, I wonder if it makes sense
to try to improve the system efficiency by relegating the SW to a manual back-up
mode only, where, say, by means of a timer controlling grid availability through
AC1, it would only charge a smaller battery bank, once a week. The bank would be
a single string of either, sealed gel units or T-105s with the new Trojan
watering system.
2) Provide new grid-tie inverter/s to handle the net metering.
3) Provide a way to AC couple the new inverter/s to the SW in the event of an
outage.
4) Provide a new Honda 3000 inverter type generator connected to AC2 in the SW.
5)Provide a way to lockout the grid tie inverter/s when the generator is
operating.
I think a few of you are still running your original SW inverters in grid tie
mode. Any upgrades? Am I going off the deep end here?
Dick Ratico