Wed Nov 9 16:55:08 EST 2011
Any amount of power will AC couple.
If you use an off grid inverter, such as an
Outback, to feed the protected load panel, the
inverter should be fed by grid AC power to supply
loads, when the grid is available. Just
feed your grid tie inverter into the protected
loads panel. You will need a relay to shut off
power from the grid tie inverter when the
batteries are full. This can be triggered by the fan relay in the Outback.
The on grid inverter will push power into the
grid through the battery inverter's internal
transfer switch during normal operation and AC
couple when the power is out. If your grid tie
inverter is 240 volts, you will need to use a transformer or two inverters.
The phantom load of the inverter can be
eliminated by using a transfer switch to send PV
power straight to the grid, during normal grid
availability, keeping the inverter turned
off. AC coupling seems much easier than using a
charge controller, but there is no conditioning
of the batteries. The charge is just on and off
at the voltage set point. For a back up system,
that is not much of a problem, as the battery
inverter can maintain the batteries when power is available.
At 02:04 PM 11/9/2011, you wrote:
>Nice Find, Drake! Thanks.
>
>What is the minimum system for an AC coupled inverter?
>
>Again, the idea is for low cost battery backup
>of an existing grid tie. The AC coupled
>schematics I have looked at require a major
>rewire and many components. I would like to hear
>if someone has a simple add on solution compared
>to just switching the array to the high voltage CC.
>
>Larry Crutcher
>Starlight Solar Power Systems
>
>
>On Nov 9, 2011, at 6:14 AM, Drake wrote:
>
>>
>>I vote for the AC coupled system. But if you
>>need to make a 600 VDC transfer switch, I think
>>you could likely make one from Tyco relays and
>>voltage controlled relays. http://relays.te.com/datasheets/ev200.pdf
>>
>>At 03:16 PM 11/7/2011, you wrote:
>>>Ray,
>>>Yes, the idea was for a low cost way to add
>>>battery backup to existing high voltage PV
>>>grid tie systems, not new construction.
>>>
>>>The second inverter does not need to be able
>>>to sell since that is handled by the grid tie
>>>inverter. It simple passes grid power to loads
>>>and maintains the battery. That means any
>>>off-grid inverter/charger or even low cost
>>>separate inverters and chargers may be used, a
>>>very economical solution. However, the idea
>>>may be of no value because it appears no one makes a transfer switch.
>>>
>>>Larry Crutcher
>>>Starlight Solar Power Systems
>>>
>>>
>>>
>>>
>>>On Nov 7, 2011, at 11:32 AM, Ray Walters wrote:
>>>
>>>>Just curious, what's the advantage of
>>>>switching at the array vs. just using a Sunny
>>>>Island or Outback system? Seems this would
>>>>cost more, and have less efficiency, since
>>>>you would still have the battery float
>>>>losses, backup inverter idle losses, in
>>>>addition to the 2nd grid tie inverter losses.
>>>>Are there site specific conditions driving this that I'm not understanding?
>>>>I've done quite a few GT systems w/ battery
>>>>backup, so I'm always up for new ideas though.
>>>>
>>>>Ray
>>>>
>>>>
>>>>On 11/7/2011 12:15 PM, Larry Crutcher,
>>>>Starlight Solar Power Systems wrote:
>>>>>Hi Glen,
>>>>>That model is a disconnect switch. What the
>>>>>system needs is a 4 pole transfer switch,
>>>>>automatic or manual, to connect the PV source to the charge controller.
>>>>>
>>>>>Hello Gary Willit,
>>>>>Yes, you've grasped my concept precisely and
>>>>>I agree, getting a high voltage DC transfer
>>>>>switch may nix this design. Sounds like a product for Midnite Solar to build.
>>>>>
>>>>>
>>>>>
>>>>>Larry Crutcher
>>>>>Starlight Solar Power Systems
>>>>>
>>>>>
>>>>>On Nov 6, 2011, at 1:42 PM, Glenn Burt wrote:
>>>>>
>>>>>>Siemens makes a line that are UL listed.
>>>>>>Their VBII series like HNF361PV 30A
>>>>>>
>>>>>>-Glenn
>>>>_______________________________________________
>>>>List sponsored by Home Power magazine
>>>>
>>>>List Address:
>>>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>>>
>>>>Options & settings:
>>>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>>
>>>>List-Archive:
>>>>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>>List rules & etiquette:
>>>>www.re-wrenches.org/etiquette.htm
>>>>
>>>>Check out participant bios:
>>>>www.members.re-wrenches.org
>>>
>>>_______________________________________________
>>>List sponsored by Home Power magazine
>>>
>>>List Address:
>>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>>
>>>Options & settings:
>>>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>List-Archive:
>>>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>>List rules & etiquette:
>>>www.re-wrenches.org/etiquette.htm
>>>
>>>Check out participant bios:
>>>www.members.re-wrenches.org
>>
>>Drake Chamberlin
>>ATHENS ELECTRIC LLC
>>OH License 44810
>>CO license 3773
>>NABCEP Certified PV
>>_______________________________________________
>>List sponsored by Home Power magazine
>>
>>List Address:
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Options & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive:
>>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>List rules & etiquette:
>>www.re-wrenches.org/etiquette.htm
>>
>>Check out participant bios:
>>www.members.re-wrenches.org
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
Drake Chamberlin
ATHENS ELECTRIC LLC
OH License 44810
CO license 3773
NABCEP Certified PV
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20111109/94642cfe/attachment.htm>
More information about the RE-Wrenches
mailing list