[RE-wrenches] High Voltage MPPT units

Ray Walters ray at solarray.com
Fri Nov 4 19:36:34 EDT 2011


Midnite Solar has the Classic 250, which can go to at least 250 v array 
open circuit plus it has an additional emergency voltage head room that 
is equal to the battery voltage. So if you had a 48 v battery, you could 
go to 298 vdc Open circuit (in extreme cold for instance) without 
damage. The Classic controller shuts off above 250 v though, so you 
don't want to design the system to operate that high, but it does give 
you some breathing room with the design.
Also on the "overkill" issue of a 1 Kw array, it all depends on the 
battery voltage. At 24 v battery, the Classic 250 can handle a maximum 
of 1722 watts. Personally I've found controllers seem to last longer 
when over sized, rather than over loaded.

Ray Walters
Solarray, Inc.

On 11/4/2011 5:22 PM, Carl Emerson wrote:
> Hi John,
>
> Yes I have seen this one thanks.
>
> I should have mentioned that the array will be about 1 kW so a unit that
> size is overkill...
>
> Carl Emerson
> Free Power Co.
> Web   www.freepower.co.nz
>
>
> -----Original Message-----
> From: re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of John
> DeBoever
> Sent: 5 November 2011 12:13 p.m.
> To: 're-wrenches at lists.re-wrenches.org'
> Subject: Re: [RE-wrenches] High Voltage MPPT units
>
> Schneider Electric just launched their MPPT 80-600, which is a 80A , up to
> 600 V.
>
> John
> Trojan Battery Company
>
> ----- Original Message -----
> From: Carl Emerson [mailto:freepower at freepower.co.nz]
> Sent: Friday, November 04, 2011 07:08 PM
> To: 'RE-wrenches'<re-wrenches at lists.re-wrenches.org>
> Subject: [RE-wrenches] High Voltage MPPT units
>
> Hi there,
>
> I have heard that Morningstar are bringing out a high voltage MPPT unit next
> year.
>
> This unit will run up to 600 Volts.
>
> In the mean time what other units are available that allow for higher than
> 150 VDC from the array.
>
> I want to avoid the expense of using a Sunnyboy at the array and bringing AC
> back to the inverter.
>
> Trying to keep cable costs down.
>
> Many Thanks,
>
> Carl Emerson
> Freepower
> Auckland NZ.
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options&  settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules&  etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
> This e-mail message and any attachments that accompany it may contain
> information that is confidential, privileged, or protected from disclosure.
>
> It is intended solely for the use of the individual(s) to whom it was
> intended
> to be addressed. If you have received this e-mail by mistake, or you are not
>
> the intended recipient, any reading, disclosure, copying or other use of
> this
> communication is strictly prohibited.  If you have received this
> communication
> in error, please immediately advise the sender at their phone number listed
> above, or by electronic mail, and also permanently delete the original and
> all
> copies of this e-mail and any attachments from all locations. Thank you.
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options&  settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules&  etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
> __________ NOD32 6602 (20111104) Information __________
>
> This message was checked by NOD32 antivirus system.
> http://www.eset.com
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options&  settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules&  etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
>



More information about the RE-Wrenches mailing list