[RE-wrenches] Feeder without a dedicated breaker

Exeltech exeltech at yahoo.com
Tue Oct 25 16:06:36 EDT 2011


William,

The tap conductor ampacity must not be less than the rating of the breaker
protecting that circuit, which in this case (if I understand the configuration
correctly) would be the main breaker in the panelboard.

Any smaller gauge would require its own OCP device of appropriate rating
if it's to be code-compliant.

Dan



--- On Tue, 10/25/11, William Miller <william at millersolar.com> wrote:

From: William Miller <william at millersolar.com>
Subject: Re: [RE-wrenches] Feeder without a dedicated breaker
To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Date: Tuesday, October 25, 2011, 2:54 PM



Jamie:


Thanks for getting me started.  I did not think to consider this as
a tap, but it appears to match the criteria.


William Miller





At 11:38 AM 10/25/2011, you wrote:

William, I would start with Article
240.21(B).


Jamie Johnson

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20111025/cfb6f90e/attachment.htm>