[RE-wrenches] ground
Ray Walters
ray at solarray.com
Sat Oct 1 01:41:24 EDT 2011
I'm a big fan of grounding at the array, and was sorry to lose 690.47D
(which also clearly allowed the structure to be considered an electrode) .
I think if you look at the sq ft. of metal in contact with the concrete,
you can make a credible case for the frame fitting the definition of an
electrode. IMHO, it's all about a low impedance path to ground. Whether
it's 20 ft of 1/2" rebar, or 4 ft of 6" diam pipe, or 4 ft of 2" x 2"
angle iron, its all roughly the same required 2 sq ft of surface area in
contact with the concrete.
Actually if you want to be a real stickler and also enforce 250.53A2, a
tough AHJ might demand 2 electrodes at the array in addition to the
structural grounding all ready present.
Me? I like the exception if the measured ground impedance is less than
25 ohm. Most inspectors will be more than satisfied, if you just show
them a quick reading with a clamp-on ground impedance tester.
What If you're still over 25 ohms? If you're in lightning country, you
really should sink another electrode anyway.
Ray
On 9/30/2011 7:04 PM, Kent Osterberg wrote:
> Ray,
>
> I believe that a pole-mounted or grounded-mounted PV array is
> considered a structure and requires a ground electrode per 250.32.
> Perhaps the exception would cover the possibility a installing very
> small system without a ground electrode.
>
> Kent Osterberg
> Blue Mountain Solar, Inc.
>
>
>
> Ray Walters wrote:
>> I've also used 250.52A(7) defining plate electrodes. A 6" Sch 40 pipe
>> 4 ft in the ground has more than the required 2 sq ft of surface
>> metal, and is at least the required 1/4" thickness.
>> Also, the 2011 NEC dropped 690.47 D which required a grounding
>> electrode at the array. Are you sure you still need this? I believe
>> 2011 only requires you bond all the metal to the EGC, as always.
>>
>> Ray Walters
>>
>> On 9/30/2011 8:24 AM, Kent Osterberg wrote:
>>> The requirements listed in 250.52(3) were changed in 2011. The rebar
>>> used is allowed to be near the bottom of the footing or in vertical
>>> foundation walls that are in direct contact with earth. If there was
>>> in doubt in the past that the rebar in the concrete of a pole mount
>>> was a suitable grounding electrode, the changes in 2011 should
>>> remove it.
>>>
>>> Kent Osterberg
>>> Blue Mountain Solar, Inc.
>>>
>>> Richard L Ratico wrote:
>>>> As Dan points out, 250.52(A)(3) specifies several installation
>>>> requirements in
>>>> order for a concrete encased electode to qualify as a permitted
>>>> Grounding
>>>> Electrode. A pole mount foundation would certainly qualify if it
>>>> met those
>>>> requirements.
>>>>
>>>> Even if the requirements are not met, IMHO, any opportunity to
>>>> inexpensively
>>>> increase the grounding integrity of a system should not be overlooked,
>>>> particularly in lightning country. Of course, a code compliant
>>>> Grounding
>>>> Electrode System is still required. Bonding a non compliant, but
>>>> never the less,
>>>> very substantial additional "electrode" to that system would not
>>>> hurt anything
>>>> and quite possibly help considerably.
>>>> Dick Ratico
>>>> Solarwind Electric
>>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
>
More information about the RE-Wrenches
mailing list