[RE-wrenches] ground

Kent Osterberg kent at coveoregon.com
Fri Sep 30 10:24:40 EDT 2011


The requirements listed in 250.52(3) were changed in 2011. The rebar 
used is allowed to be near the bottom of the footing or in vertical 
foundation walls that are in direct contact with earth. If there was in 
doubt in the past that the rebar in the concrete of a pole mount was a 
suitable grounding electrode, the changes in 2011 should remove it.

Kent Osterberg
Blue Mountain Solar, Inc.

Richard L Ratico wrote:
> As Dan points out, 250.52(A)(3) specifies several installation requirements in
> order for a concrete encased electode to qualify as a permitted Grounding
> Electrode. A pole mount foundation would certainly qualify if it met those
> requirements.
>
> Even if the requirements are not met, IMHO, any opportunity to inexpensively
> increase the grounding integrity of a system should not be overlooked,
> particularly in lightning country. Of course, a code compliant Grounding
> Electrode System is still required. Bonding a non compliant, but never the less,
> very substantial additional "electrode" to that system would not hurt anything
> and quite possibly help considerably. 
>
> Dick Ratico
> Solarwind Electric
> _______________________________________________
>   


More information about the RE-Wrenches mailing list