[RE-wrenches] Help me understand Gen vs XW

jay peltz jay at asis.com
Fri Sep 9 10:36:55 EDT 2011


Hi William,

is the problem the actual connection or the AGS?

if its the actual connection, have you tried putting a load ( say 1000 watt heater) on the generator directly  to stabilize the volt/hz from the genny?
if for a test if nothing else.

jay

peltz power

On Sep 8, 2011, at 9:40 PM, William Miller wrote:

> Friends:
> 
> Working yesterday on a newer XW system with a new Kohler RES15 generator.  This is the first time I have tested the inverter with this generator.  The inverter would not maintain a transfer to the generator.  After about an hour on the phone with tech support, the tech searched previous calls and announced that there is a known incompatibility between the Kohler RES15 and a certain version of the XW firmware.  I was advised to upgrade the firmware.
> 
> I wonder how this can be.  Voltage and frequency even in the moment the inverter did try to connect are well within specifications. After some thought, all I can guess is that there might be some noise on the AC signal that the inverter might reject.
> 
> Has anyone else experienced this?  Any insight to be offered?
> 
> Thanks in advance.
> 
> William Miller
> 
> William Miller 
> Miller Solar
> Voice :805-438-5600
> email: william at millersolar.com
> http://millersolar.com
> License No. C-10-773985
> 
> 