[RE-wrenches] unique battery bank design question
Rob Shappell
rob at nwes.com
Fri Sep 2 09:53:43 EDT 2011
As far as I know, The DC/DC and the Equalizers do basically the same thing
(step up or down). I recollect that the Equalizers are adjustable and can be
used as a load dump. Enermaxer comes to mind. It's been a long time.......
but a refresher will be gladly accepted from those in the know.
Rob Shappell
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Friday, September 02, 2011 9:42 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] unique battery bank design question
Yeah, Rob, you and I have talked about this before regarding 12V required
for generator start/control with a 48V battery bank. In that case we did the
inefficient thing by charging the generator starting battery with a 12V
charger off the AC output of the inverter. A separate PV panel was the more
expensive option. I appreciate your input on this.
What can you tell us about battery equalizers as an alternative to DC-DC
converters??
Jason Szumlanski
Fafco Solar
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Rob Shappell
Sent: Friday, September 02, 2011 8:24 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] unique battery bank design question
I never, never recommend taps of any sort, but sometimes we have to satisfy
the needs of the customer. If any taps are done in any manner I would
recommend AT LEAST an annual reconfig of the taps.
To reduce and/or eliminate the imbalance of the 12 volt and 24 volt taps,
you could install a 12 volt charging source to the 12 volt tap, a 24 volt
charging source to the 24 volt tap and the 48 volt loads get a 48 volt
charging source. The array is still calculated the same, just distributed
different through different controllers. Is this bullet proof or perfect?
Nope, but neither are DC/DC converters and the system is much more efficient
too.
Rob Shappell
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list