[RE-wrenches] mechanical vs. electronic kwh meter
Jason Szumlanski
Jason at fafcosolar.com
Fri Aug 12 12:08:58 EDT 2011
That is absolutely true. We have a customer who sent in his
interconnection agreement and assumed the meter would be swapped. It
never happened, the utility did not swap the meter, and energy sold to
the utility actually showed up as purchased energy. The utility
acknowledged the oversight in getting the meter swapped, and they are
working with the customer on an equitable resolution.
That is definitely a reason consider keeping the system off until the
meter is swapped, but then you are relying on the customer to go flip
the switch once installed.
Jason Szumlanski
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dave
Click
Sent: Friday, August 12, 2011 11:15 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] mechanical vs. electronic kwh meter
I just asked a guy I know in utility metering, and he confirms that
there's no basis for the utility's concern. Their claim that backfeeding
is a safety hazard could be an attempt to dissuade some non-PV folks
from flipping their meters to steal power. Or that could be their
justification to charge the customer for the new electronic meter (some
utilities do this, apparently).
As an anti-theft precaution, some mechanical meters don't actually spin
backwards- so whether you're importing or exporting a 1kW, after an hour
your counter has ticked up by one. So just because it's a mechanical
meter doesn't mean that you should necessary leave it running until the
utility installs that bidirectional electronic meter.
On 2011/8/12 9:45, Kirk Herander wrote:
> Hello,
>
> I am now in a debate with the metering dept. of a local utility. They
> don't want a PV system to be energized and tested until a
bidirectional
> electronic meter is installed. They insist that an old plain Jane
> mechanical meter can be damaged and is a safety concern if power is
> pushed through it (its running backwards) to the grid. I have never
> heard of, witnessed, or been told this by any utility or AHJ inspector
> until now. Have any of you ever?
>
> I don't know the reason for their paranoia. I assume that many utility
> districts don't to this day install bidirectional electronic meters.
And
> rely on the original mechanical meter to count backwards reliably and
> safely.
>
> Kirk Herander
>
> VT Solar, LLC
>
> dba Vermont Solar Engineering
>
> NABCEP^TM Certified installer Charter Member
>
> NYSERDA-eligible Installer
>
> VT RE Incentive Program Partner
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options& settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules& etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list