[RE-wrenches] 2 SW inverters on three phase

boB Gudgel boB at midnitesolar.com
Thu Jul 28 13:56:07 EDT 2011



Do you just want to charge batteries  and are these regular  120VAC SWs 
??   120/208 ??

If so, you should just be able to connect each  SW from neutral to hot. 
No stacking necessary.

A regular SW stacking cable won't work for delta connections because 
that assumes
the phases are going to be 180 degrees (120/240) and not 120 degrees as  
for 208V delta.

There was a 3 phase version of the SWs which required a separate 3-way 
cable and
different software in the SW itself.

boB




> On Thu, Jul 28, 2011 at 12:23 AM, William Miller 
> <william at millersolar.com <mailto:william at millersolar.com>> wrote:
>
>     Friends:
>
>     Is there any way to connect two SW series inverters to two phases
>     of a three phase generator?  It seems to me that one could connect
>     three SW inverters with the right stacking cable (or am I
>     confusing Outback inverters with the hub jumper set properly).
>
>     Any input is appreciated.
>
>     Thanks,
>
>     William
>
>     William Miller
>     Miller Solar
>     Voice :805-438-5600 <tel:805-438-5600>
>     email: william at millersolar.com <mailto:william at millersolar.com>
>     http://millersolar.com
>     <http://millersolar.com/>License No. C-10-773985
>
>
-------------- next part --------------