My experience with the M190 ac connector is this: It is possible to join the
two connector halves and rotate the cuff sufficiently to establish an
electrical connection. But if you don't rotate the cuff until the detant is
engaged, you may not completely seal the connection by compressing the
internal face gasket.
I really haven't looked into it much further but I wonder if the water you
observed entered through an incomplete connector mate, along the conductors,
into the inverter enclosure?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_____
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Kirk
Herander
Sent: Friday, June 17, 2011 4:51 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Enphase Nema 6 enclosure - not
yes
Kirk Herander
VT solar, LLC
dba Vermont Solar Engineering
NABCEPTM Certified installer Charter Member
NYSERDA-eligible Installer
VT RE Incentive Program Partner
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Thursday, June 16, 2011 11:28 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Enphase Nema 6 enclosure - not
Was that an M190?
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_____
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Kirk
Herander, VSE
Sent: Thursday, June 16, 2011 6:50 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Enphase Nema 6 enclosure - not
I just figured out why I could not reset a GFI error on one of my
micro-inverters. First, I noticed condensation in the led lens, then water
literally dripped out of the AC side as soon as I disconnected it. This was
mounted on the top backside of a panel, roughly two ft above a flat roof.
... fascinating
Kirk Herander
Vermont Solar Engineering
802.863.1202 fax 802.863.7908
VT RE Incentive Program Partner
NYSERDA Incentive-eligible Partner
NABCEPTM Certified Installer
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20110617/ee6cfa4f/attachment.htm>
More information about the RE-Wrenches
mailing list