It seems like it should be fine if you run one conduit to your shop inverter, 
and another to a dc disconnect and underground to the house inverter, but I see 
you running a bonding wire for the 2 GECs as well for some reason. You should go 
through the part of 250 about different GEC for separate building, which has 
some optional installation options, and you could likely use that to justify 
running the equipment ground back to the house.