[RE-wrenches] sizing a sub-panel used to combine multiple inverter outputs
Mark Frye
markf at berkeleysolar.com
Wed Mar 30 01:16:38 EDT 2011
I think Kent and I agree. For the case where the subpanel is not dedicated a
PV sub-panel he is calculating for 2 - 50A breakers and I calculated for 3 -
50A breakers.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
<http://www.berkeleysolar.com/> www.berkeleysolar.com
_____
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Tuesday, March 29, 2011 9:26 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multiple
inverter outputs
Per 705.12(D) the sub-panel could be any distribution equipment on the
premises. So the question becomes: is the sub-panel capable of supplying
branch circuits or feeder loads? If yes, then the sum of the breakers
(potentially) feeding the bus is 180 amps so a 150-amp rating is required
and the inverters would have to feed the opposite end of the bus bars. If
no, the code is not clear on the requirement, but obviously the 80-amp
breaker in the main panel limits the maximum current flowing through the
sub-panel.
Kent Osterberg
Blue Mountain Solar
-------------- next part --------------