[RE-wrenches] grounding the Enphase inverter
Bill Brooks
billbrooks7 at yahoo.com
Fri Mar 4 12:51:28 EST 2011
System grounding requirements.
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Friday, March 04, 2011 7:51 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter
The interesting thing to me is the underlying assumption in the Code that a
GEC is requried for grid-tied inverters at all. Why isn't EG sufficient for
function and safety.
Which of the following common electrical equipment has the same requirement:
UPS
Motors with regenerative energy disipators
DC power supplies
Standby generators
??
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent: Thursday, March 03, 2011 10:48 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter
All,
While there is ambiguity in the 2008 NEC in 690.47(C) on the requirements
for system grounding of PV systems, the 2011 NEC in 690.47(C) clarifies the
intent.
While an application note from Enphase may state that WEEBs can be used as
part of the grounding electrode system, I disagree with this concept and do
not believe it meets the requirements or intent of the NEC as clarified in
the 2011 NEC. The problem with a grounded PV inverter is that it requires a
grounding electrode conductor (GEC) from the grounding point (on the
inverter) to the grounding electrode. The 2008 and 2011 NEC allows for that
connection to be terminated at the grounding bar in the service panel
supplying the micro-inverters.
There is no problem with using the WEEB to bond the rails to the modules and
then to the Enphase Micro-inverter. From the micro-inverter, a bare 6AWG
could be run to pick up each micro-inveter in each row of micro-inverters
with splices made to a single bare 6AWG made with irreversible splices. At
the rooftop junction box, the GEC could be irreversibly spliced to an 8AWG
green insulated conductor to run unbroken to the grounding busbar in the
service equipment.
While this may not be in agreement with the Enphase application note, I
believe it meets the intent and letter of the NEC as clarified in the 2011
NEC 690.47(C). While using the WEEBs in the GEC circuit may not cause a life
or death issue, it is absolutely open to being questioned by the electrical
inspector. If the electrical inspector decides it is wrong--it is wrong. If
you or the field inspector appeals to me or an expert like John Wiles, we
will state what I have stated above. Then you would have to remove all the
modules, throw away the WEEBs, put in new WEEBs with the new bare copper
6AWG and reinstall the modules--it just ain't worth it.
690.47(D) was removed from the 2011 NEC because it was primarily for
lightning protection (not a safety issue according to the NEC) and was
ambiguously worded with respect to residential rooftop PV systems. If the
local jurisdiction requires the additional electrode, install a j-box at the
point near ground-level where the conduit transitions from vertical to
horizontal and install an irreversibly spliced bare 6AWG to run from the
j-box to a ground rod below the j-box--mildly painful, but very doable.
Bill.
Bill Brooks, PE
Principal
Brooks Engineering
873 Kells Circle
Vacaville, CA 95688
707-332-0761 (office and mobile)
707-451-7739 (fax)
bill at brooksolar.com (email)
www.brooksolar.com (web)
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list