Karl -
Is this instant excess or excess during a specific billing
period?
Does this violate Federal regulations?
Could you divert or bank the excess in process heat, water
pumping, or some other function?
Dana Orzel
Great Solar Works, Inc
E - dana at solarwork.com
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076
web - www.solarwork.com
"Responsible Technologies for Responsible People since 1988"
Do not ever believe anything, but seriously trust through
action.
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf
Of Karl Jaeger
Sent: Tuesday, February 15, 2011 3:21 PM
To: re-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] "Keep that there PV off my grid!"
Greetings Esteemed Wrenches,
My company was recently tasked to engineer a PV project in
Alabama. We sat down for a meeting with all of the local
big-shots. They proceeded to let us know that we are not
allowed to feed any excess PV power onto their grid,
production cannot exceed demand. I am hoping that y'all
might be able to steer me towards a contactor assembly or
device that would detect reverse current flow, trigger the
contactor, then open up the inverter AC output circuit. The
service is 3-phase, 208 volt. The maximum current we intend
to introduce is 70 amps, continuous.
Appreciate your advice,
Karl Jaeger
Operations Manager
LightWave Solar Electric
www.lightwavesolar.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20110215/90b7bac7/attachment.htm>
More information about the RE-Wrenches
mailing list